grounding electrode question #179372 07/09/08 09:19 PM
Joined: May 2003
Posts: 17
B
barbwire Offline OP
Junior Member
Hello All, I'm planning on installing a new 200 Amp service to my house in the near future, unfutunately I need to add a new concrete walk on the service side of the house before the service, If I drive down 2 rods 6-7 ft apart, #4 between them and to the panel ,can I cover them with the walk?(no visual inspection possible). leaving them above would become a tripping hazard. Any Ideas?

2017 / 2014 NEC & Related Books and Study Guides
Re: grounding electrode question [Re: barbwire] #179373 07/09/08 09:26 PM
Joined: Jul 2004
Posts: 9,383
G
gfretwell Offline
Member
250.68 Grounding Electrode Conductor and Bonding Jumper Connection to Grounding Electrodes.
(A) Accessibility. The connection of a grounding electrode conductor or bonding jumper to a grounding electrode shall be accessible.
Exception: An encased or buried connection to a concrete-encased, driven, or buried grounding electrode shall not be required to be accessible.


Greg Fretwell
Re: grounding electrode question [Re: gfretwell] #179374 07/09/08 09:59 PM
Joined: May 2003
Posts: 17
B
barbwire Offline OP
Junior Member
So an inspector would have no proof that the job was done properly?

Re: grounding electrode question [Re: barbwire] #179375 07/09/08 10:18 PM
Joined: Jul 2004
Posts: 9,383
G
gfretwell Offline
Member
That is always going to be the case with a buried or concrete encased electrode if it was existing when you do the upgrade.
Call the AHJ and see if they will be happy with pictures or pull your permit now and have the GEC inspected on a partial rough. How long will it be before you do the upgrade?


Greg Fretwell
Re: grounding electrode question [Re: barbwire] #179376 07/09/08 10:32 PM
Joined: Aug 2007
Posts: 853
L
leland Offline
Member
Originally Posted by barbwire
So an inspector would have no proof that the job was done properly?


This would fall under the "under ground" inspection.
Meaning it must be inspected before backfilling it.
This is a standard here, perhaps not every where.

Re: grounding electrode question [Re: leland] #179384 07/10/08 09:29 AM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
A question here ....

Would not a Ufer in the walk be a superior grounding electrode to a driven rod - and easier to instal as well?

Re: grounding electrode question [Re: renosteinke] #179386 07/10/08 11:46 AM
Joined: Mar 2005
Posts: 399
A
Alan Nadon Offline
Member
The sidewalk would need to have a "footer" for a Ufer to be effective. With only a few inches of concrete above it would tend to be in a dry area.
Pull the permit early have the grounding rods and interconnect inspected and approved, then cover with the sidewalk. Make sure to have it noted on the permit or get a copy of the inspection report in case the inspector can't remember or you get a different inspector.
Just a point to remember: If you can make them fit, the ground rods can be installed INSIDE the building. This also elliminates the copper theives from cutting your wire.


Alan--
If it was easy, anyone could do it.
Re: grounding electrode question [Re: Alan Nadon] #179399 07/10/08 07:49 PM
Joined: May 2003
Posts: 17
B
barbwire Offline OP
Junior Member
Thanks for the input, sounds like I need to get this permit pulled earlier than expected, to be on the safe side. Thanks ALL.

Re: grounding electrode question [Re: barbwire] #179401 07/10/08 08:43 PM
Joined: Jul 2004
Posts: 9,383
G
gfretwell Offline
Member
The only downside is since they are out there they might want a permit for the sidewalk. Things are pretty slow down at the building department so they are drumming up business where they can.


Greg Fretwell
Re: grounding electrode question [Re: gfretwell] #179438 07/13/08 06:11 PM
Joined: Jul 2007
Posts: 85
W
WireNuts29 Offline
Member
I'm not sure about the sequence of events in your area. If I pull a permit to change a service. I must have in hand the SER # from the utility, to put on the permit. This is the utilities authorization # to break the seal on the meter. The catch 22 is you have to complete the upgrade within 90 days of pulling the number from utility. upon inspection by local inspector they will reseal meter, and put their crimp on connectors. In your case I'd suggest you pull a permit, and have it inspected for what it is a grounding electrode, leave the service change permit for when you actually do that. make sure you explain to the inspector your intentions. That would be the best course of action in my neck of the woods.

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 23
GeneSF 8
Popular Topics(Views)
257,933 Are you busy
193,663 Re: Forum
183,281 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3