2 phase services #179233 07/02/08 11:26 AM
Joined: Apr 2007
Posts: 36
J
junkcollector Offline OP
Member
This topic has probably been brought up here before, but through some searching I found nothing. (Sorry if I'm beating a dead horse sleep )

My question is, has anyone worked in a building that had 2 phase power? Was it POCO supplied, if so, could you explain the transformer hookup? (If overhead) What kind of disconnects / panelboards where used? I seen a few pictures of a smaller 2 phase service on a home inspector site. I consisted of 2 FPE panelboards, both feed with 2 hots and shared a nuetral. The meter said 2 phase, 5 wire. It had 5 wires for a utility drop. (Pics didn't show transformer hookup)

Just wondering if anyone had any information or examples on what a service consisted of. I know this is pretty much an obsolete system, but may well still exist in larger cities so it would be interesting to know how modern components, panelboards, etc are connected. I have seen diagrams and schematics for a Scott-T connection, and the theoretical aspects of changing 3 phase to 2 phase make sense, I was more or less wondering about the physical aspects.

Thanks everyone for any tidbits you can provide. smile

Work Gear for Electricians and the Trades
Re: 2 phase services [Re: junkcollector] #179242 07/02/08 08:30 PM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
I have seen diagrams in literature from Cooper Power Systems and in Ugly's book.

The common conductor needs to be sized very carefully. On a standard 2-phase 3-wire circuit the common conductor needs to be 1.414x the line conductors.

Re: 2 phase services [Re: JBD] #179255 07/03/08 02:18 PM
Joined: Dec 2005
Posts: 860
R
RODALCO Offline
Member
The meter 2 phase 5 wire has the following terminals.

Phase 1 line
Phase 1 load
Phase 2 line
Phase 2 load
Neutral

so 5 wires are used.


The product of rotation, excitation and flux produces electricty.
Re: 2 phase services [Re: RODALCO] #179305 07/05/08 08:27 PM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
Originally Posted by RODALCO
The meter 2 phase 5 wire has the following terminals.

Phase 1 line
Phase 1 load
Phase 2 line
Phase 2 load
Neutral

so 5 wires are used.


A 2-phase 5-wire system is basically (2) 3-wire systems, loads were never connected between Phase 1 and Phase 2.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
MCosta 3
Popular Topics(Views)
275,509 Are you busy
209,408 Re: Forum
196,796 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3