I've done T-5, 4-tube low-bays before and I seem to remember the white & grey ballast lead connected together at the factory with a push-in connector and a lead coming off to connect to the neutral of the supply
Is this correct?
I saw another brand that has black, white and gray, but they show the supply neutral connected to the white ballast lead, and also feeding a switch that connects the grey lead to the whites.
Is this just to switch 2 of the lamps separately?
If so, why is the switch loop in the neutral?
Thanks
|
|
|
|
Joined: Mar 2001
Posts: 2,056
OP
Member
|
42 views and no opinions?
I forgot to mention that it is a single ballast for 4 lamps.
Last edited by Redsy; 04/22/08 07:29 AM.
|
|
|
|
Joined: Apr 2002
Posts: 7,371 Likes: 7
Member
|
Redsy: OK, I'm the 43rd view, but sorry to say I can't help you on this.
John
|
|
|
|
Joined: Dec 2000
Posts: 4,293
Member
|
#49 here......Redsy, do you know the manufacturer?
|
|
|
|
Joined: Sep 2005
Posts: 421
Member
|
although have installed a bunch of them I never looked inside at the ballast(s) until recently these 4 light Stoncos use a three lamp and single lamp ballast, which makes switching inside/outside impossible... so I am no help
I just assumed the electronic ballasts had no color code standards
I was actually stunned at the replacement cost of the three lamp unit..>$90
Tom
|
|
|
|
Joined: Mar 2007
Posts: 3
New Member
|
I just finished installing several of these fixtures and the white and gray wire went to the neutral.I;m not sure why,but that's the only all 4 lamps would come on.
Work Safe
|
|
|
|
Joined: Jan 2001
Posts: 1,044
Member
|
Working from a rather feeble memory, if you connect the grey wire to the neutral (and possibly the hot) all 4 lamps will come on when power is applied to the fixture. The gray can be run through a motion sensor or other control device to provide dual level lighting.
Tom
Few things are harder to put up with than the annoyance of a good example.
|
|
|
|
Joined: Jan 2006
Posts: 558
Member
|
I have installed these fixtures before and yes it is to be able to switch 2 or 3 of the lamps independently.. WHY they choose to do this with the neutral puzzles me, but as far as I know and have read, this is the purpose of the grey wire.
I think perhaps it is intended for some sort of optional "occupancy sensing" system, where 1 or 2 out of 4 lights normally burn constantly but the remaining lamps are fired up when a person or object moves in the area below the fixture.
A.D
|
|
|
|