Posted By: Redsy T-5 white & grey wire - 04/21/08 11:32 PM
I've done T-5, 4-tube low-bays before and I seem to remember the white & grey ballast lead connected together at the factory with a push-in connector and a lead coming off to connect to the neutral of the supply

Is this correct?

I saw another brand that has black, white and gray, but they show the supply neutral connected to the white ballast lead, and also feeding a switch that connects the grey lead to the whites.

Is this just to switch 2 of the lamps separately?

If so, why is the switch loop in the neutral?

Thanks
Posted By: Redsy Re: T-5 white & grey wire - 04/22/08 11:27 AM
42 views and no opinions?

I forgot to mention that it is a single ballast for 4 lamps.
Posted By: HotLine1 Re: T-5 white & grey wire - 04/22/08 12:14 PM
Redsy:
OK, I'm the 43rd view, but sorry to say I can't help you on this.
Posted By: electure Re: T-5 white & grey wire - 04/22/08 12:47 PM
#49 here......Redsy, do you know the manufacturer?

Posted By: togol Re: T-5 white & grey wire - 04/22/08 06:34 PM
although have installed a bunch of them I never looked inside at the ballast(s) until recently these 4 light Stoncos use a three lamp and single lamp ballast, which makes switching inside/outside impossible... so I am no help

I just assumed the electronic ballasts had no color code standards

I was actually stunned at the replacement cost of the three lamp unit..>$90
Posted By: oletimer Re: T-5 white & grey wire - 04/22/08 08:54 PM
I just finished installing several of these fixtures and the white and gray wire went to the neutral.I;m not sure why,but that's the only all 4 lamps would come on.
Posted By: Tom Re: T-5 white & grey wire - 04/22/08 09:47 PM
Working from a rather feeble memory, if you connect the grey wire to the neutral (and possibly the hot) all 4 lamps will come on when power is applied to the fixture. The gray can be run through a motion sensor or other control device to provide dual level lighting.

Tom
Posted By: Rewired Re: T-5 white & grey wire - 04/22/08 09:51 PM
I have installed these fixtures before and yes it is to be able to switch 2 or 3 of the lamps independently.. WHY they choose to do this with the neutral puzzles me, but as far as I know and have read, this is the purpose of the grey wire.