Tray Cables into Mcc's termination methods??? #175876 03/13/08 04:46 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
I;ve seen Chase nipples put into the top of Mcc's (in wireways only) then several Tray cables run into them . I told the conmtractor I didn't feel this was a approved termintation method. I;ve seen Nipples from Mcc's up to the tray (lest them 24inches . But never Chase nipples?? My concern was even thought the nipples open into the wireways it leaves an unprotected opening.YER opinions Please.
YoopersUp

2017 / 2014 NEC & Related Books and Study Guides
Re: Tray Cables into Mcc's termination methods??? [Re: Yoopersup] #175878 03/13/08 05:24 PM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
I have seen what you describe. The wiring trough area of MCC's (for load conductors) does not provide direct access to any energized parts, I would be more concerned with securing the TC.

Re: Tray Cables into Mcc's termination methods??? [Re: JBD] #175882 03/13/08 06:16 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
The drop from the tray to the Mcc's is only about 24-36 inches Max.what about 392.8(c)

Re: Tray Cables into Mcc's termination methods??? [Re: Yoopersup] #175884 03/13/08 07:30 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
Take a look at 312.5(C) and 314.17(B).


Don(resqcapt19)
Re: Tray Cables into Mcc's termination methods??? [Re: resqcapt19] #175887 03/13/08 08:27 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
But does a MCC come into play in that section??

Re: Tray Cables into Mcc's termination methods??? [Re: Yoopersup] #175997 03/17/08 06:55 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
In my opinion, between Articles 312 and 314, all electrical enclosures are covered.


Don(resqcapt19)
Re: Tray Cables into Mcc's termination methods??? [Re: resqcapt19] #176032 03/18/08 05:27 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
The Scope sections 312.1 & 314.1 says otherwise.

Re: Tray Cables into Mcc's termination methods??? [Re: Yoopersup] #176121 03/20/08 08:04 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
I think that I can stretch the scope of 314 to cover just about any electrical enclosure including MCCs.


Don(resqcapt19)
Re: Tray Cables into Mcc's termination methods??? [Re: resqcapt19] #176144 03/21/08 07:25 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
314 No way. 312 you'd have to use 90.4 and I really think you'd be streaching it. Which one is it a Cabinet(see definitions) Cut out box (No), Meter Socket encloser (No).
So then a MCC must be a Cabinet .
Cabinet (an encloser that is designed for either surface mounting or flush mounting and is provided with a frame ,mat, or trim in which a swinging door or doors are or can be hung. Doesn;t sound like a MCC does it??

Re: Tray Cables into Mcc's termination methods??? [Re: Yoopersup] #176160 03/22/08 10:12 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
The part of the MCC that you run the cables into is used as a pull box.
Quote
314.1 Scope
This article covers the installation and use of all boxes and conduit bodies used as outlet, device, junction, or pull boxes, depending on their use, and handhole enclosures.


Don(resqcapt19)

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 2
andey 2
Popular Topics(Views)
261,342 Are you busy
196,509 Re: Forum
185,761 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3