Tray Cables into Mcc's termination methods???
#175876
03/13/08 05:46 PM
|
Joined: Mar 2003
Posts: 849
OP
Member
|
I;ve seen Chase nipples put into the top of Mcc's (in wireways only) then several Tray cables run into them . I told the conmtractor I didn't feel this was a approved termintation method. I;ve seen Nipples from Mcc's up to the tray (lest them 24inches . But never Chase nipples?? My concern was even thought the nipples open into the wireways it leaves an unprotected opening.YER opinions Please. YoopersUp
|
|
|
Re: Tray Cables into Mcc's termination methods???
[Re: Yoopersup]
#175878
03/13/08 06:24 PM
|
Joined: Jul 2001
Posts: 599
Member
|
I have seen what you describe. The wiring trough area of MCC's (for load conductors) does not provide direct access to any energized parts, I would be more concerned with securing the TC.
|
|
|
Re: Tray Cables into Mcc's termination methods???
[Re: JBD]
#175882
03/13/08 07:16 PM
|
Joined: Mar 2003
Posts: 849
OP
Member
|
The drop from the tray to the Mcc's is only about 24-36 inches Max.what about 392.8(c)
|
|
|
Re: Tray Cables into Mcc's termination methods???
[Re: Yoopersup]
#175884
03/13/08 08:30 PM
|
Joined: Nov 2000
Posts: 2,148
Member
|
Take a look at 312.5(C) and 314.17(B).
Don(resqcapt19)
|
|
|
Re: Tray Cables into Mcc's termination methods???
[Re: resqcapt19]
#175887
03/13/08 09:27 PM
|
Joined: Mar 2003
Posts: 849
OP
Member
|
But does a MCC come into play in that section??
|
|
|
Re: Tray Cables into Mcc's termination methods???
[Re: Yoopersup]
#175997
03/17/08 07:55 PM
|
Joined: Nov 2000
Posts: 2,148
Member
|
In my opinion, between Articles 312 and 314, all electrical enclosures are covered.
Don(resqcapt19)
|
|
|
Re: Tray Cables into Mcc's termination methods???
[Re: resqcapt19]
#176032
03/18/08 06:27 PM
|
Joined: Mar 2003
Posts: 849
OP
Member
|
The Scope sections 312.1 & 314.1 says otherwise.
|
|
|
Re: Tray Cables into Mcc's termination methods???
[Re: Yoopersup]
#176121
03/20/08 09:04 PM
|
Joined: Nov 2000
Posts: 2,148
Member
|
I think that I can stretch the scope of 314 to cover just about any electrical enclosure including MCCs.
Don(resqcapt19)
|
|
|
Re: Tray Cables into Mcc's termination methods???
[Re: resqcapt19]
#176144
03/21/08 08:25 PM
|
Joined: Mar 2003
Posts: 849
OP
Member
|
314 No way. 312 you'd have to use 90.4 and I really think you'd be streaching it. Which one is it a Cabinet(see definitions) Cut out box (No), Meter Socket encloser (No). So then a MCC must be a Cabinet . Cabinet (an encloser that is designed for either surface mounting or flush mounting and is provided with a frame ,mat, or trim in which a swinging door or doors are or can be hung. Doesn;t sound like a MCC does it??
|
|
|
Re: Tray Cables into Mcc's termination methods???
[Re: Yoopersup]
#176160
03/22/08 11:12 PM
|
Joined: Nov 2000
Posts: 2,148
Member
|
The part of the MCC that you run the cables into is used as a pull box. 314.1 Scope This article covers the installation and use of all boxes and conduit bodies used as outlet, device, junction, or pull boxes, depending on their use, and handhole enclosures.
Don(resqcapt19)
|
|
|
|
|