I found this on a fire department site, they were questioning ladder access to the side of the building, where the POCO feed is run along the side of a building. Are there any code problems presented with this installation? http://www.vententersearch.com/?p=232
|
|
|
Re: Feeder run along outside
[Re: JCooper]
#175771
03/10/08 11:34 PM
|
Joined: Jul 2004
Posts: 9,571
Member
|
It appears to be more that 3' from all of the windows and plenty high enough off the ground so I don't see a code violation there but you may have a problem with the disconnects not being "grouped". I can't tell how they are arranged
Greg Fretwell
|
|
|
Re: Feeder run along outside
[Re: gfretwell]
#175777
03/11/08 08:47 AM
|
Joined: Aug 2002
Posts: 402
Member
|
What about that gutter downspout that runs behind the wires. Unless it is some type of platic pipe it looks like a disaster waiting to happen when the pipe becomes energised.
|
|
|
Re: Feeder run along outside
[Re: jdevlin]
#175792
03/11/08 04:37 PM
|
Joined: May 2006
Posts: 29
Junior Member
|
. There are no code violations. The Open wiring on insulators as per 230.43 are/is not POCO. They are service entrance.
As for the FD concerns. They will have to overcome, adapt and improvise.
|
|
|
|
|