#175307 - 02/26/08 08:20 PM 70E Where stickers (Not 110.16) not 110.16 sticker  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 831
Michigan
NFPA says Hazard Analysis anything operationing at over 50 volts . That Means Mcc's, Switchgear, Panels 120/208
277/480 & up and up. I take it that includes Panels and Equipment over 50 volts Period. Example PLC 120 volt feed??
fire alarm Panel. 120/240 volt feed.
X ray Machine ect ect. Where is the Break Line and where in 70E does it say the break line is?? NEC 110.16 Spells out where ist sticker goes . 70E from what I see Doesn't where second one is required except Fer Hazard analysis. 2008 NEC adds Electrical Equipment to 110.16.look up equipment in definations in NEC umm this gets interesting??


Arc Flash PPE Clothing, LOTO & Insulated Tools

#175310 - 02/26/08 09:39 PM Re: 70E Where stickers (Not 110.16) not 110.16 sticker [Re: Yoopersup]  
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
NFPA70E does not require any sticker/lables in addition to those in NEC 110.16.

70E requires appropiate PPE for all energized work above 50V. There is no relief.

There are several options available for determing the appropiate PPE, a full blown "arc flash" study based on IEEE 1584 is only one method.


#175322 - 02/26/08 10:37 PM Re: 70E Where stickers (Not 110.16) not 110.16 sticker [Re: JBD]  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 831
Michigan
All over 50 volts covers a lotta ground.


#175324 - 02/26/08 10:49 PM Re: 70E Where stickers (Not 110.16) not 110.16 sticker [Re: Yoopersup]  
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Originally Posted by Yoopersup
All over 50 volts covers a lotta ground.


Yasure youbetcha.
Luckily, appropiate PPE is rarely a 40 cal "moon suit".


#175326 - 02/26/08 11:04 PM Re: 70E Where stickers (Not 110.16) not 110.16 sticker [Re: JBD]  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 831
Michigan
But Like lets say you open a Fire alarm Pnl/ 120/240 >
voltage test ist with PPE on??? Sticker on Box??


#175327 - 02/26/08 11:13 PM Re: 70E Where stickers (Not 110.16) not 110.16 sticker [Re: Yoopersup]  
frenchelectrican  Offline
Member
Joined: Feb 2003
Posts: 939
Wi/ Paris France { France for ...
Originally Posted by Yoopersup
But Like lets say you open a Fire alarm Pnl/ 120/240 >
voltage test ist with PPE on??? Sticker on Box??


That is good question because if my memory serve me right most FA panels are pretty much current limited type.

Merci, Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


#175329 - 02/26/08 11:41 PM Re: 70E Where stickers (Not 110.16) not 110.16 sticker [Re: frenchelectrican]  
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
There is no IEEE 1584 calculation for single phase circuits regardless of voltage so they are not normally part of arc flash studies therefore they rarely have a cal/cm² sticker on them.

If the calories or Hazard Risk Category (HRC) are not known you are only left with the 70E task tables. If the circuits are current limiting then you may be able to take advantage of the provisions that allow a reduction in the normal task table HRC.

How come the Wisconsin and UP guys are up at this time of night, don't you have to get up and shovel in the morning?


#175330 - 02/26/08 11:53 PM Re: 70E Where stickers (Not 110.16) not 110.16 sticker [Re: JBD]  
frenchelectrican  Offline
Member
Joined: Feb 2003
Posts: 939
Wi/ Paris France { France for ...
JBD.,, This topic is almost parallel in other forum as well but not the excat same sisuation but i feel pretty simuair what you are talking about the Flash protection requirement need.


speaking of snow i only got dusting of snow [ about 30 CM or so { 1 1/2 inch } but right now it kinda windy now just got back from service call not too long ago the road start to get icy again ughh.

Merci, Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


#175343 - 02/27/08 07:38 AM Re: 70E Where stickers (Not 110.16) not 110.16 sticker [Re: frenchelectrican]  
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
Originally Posted by JBD
Originally Posted by Yoopersup
All over 50 volts covers a lotta ground.


Yasure youbetcha.
Luckily, appropiate PPE is rarely a 40 cal "moon suit".
PPE for 51V is a cotton shirt and dry hands, isn't it?


#175356 - 02/27/08 06:57 PM Re: 70E Where stickers (Not 110.16) not 110.16 sticker [Re: SteveFehr]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,124
Estero,Fl,usa
How many amps Steve?


Greg Fretwell

Page 1 of 3 1 2 3

Member Spotlight
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
Posts: 30
Joined: January 2013
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.025s Queries: 16 (0.004s) Memory: 0.8216 MB (Peak: 1.0007 MB) Zlib enabled. Server Time: 2017-10-23 22:45:09 UTC