Bathroom exhaust fans #174480 02/05/08 09:46 PM
Joined: Nov 2005
Posts: 186
HCE727 Offline OP
Member
Do bathroom exhaust fans have to be switched with the lighting or can they be individually switched?


Hank
Work Gear for Electricians and the Trades
Re: Bathroom exhaust fans [Re: HCE727] #174483 02/05/08 10:15 PM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline
Member
Unless some local ordinance requires it, I can't think of any requirement to have them come on at the same time.


Re: Bathroom exhaust fans [Re: Redsy] #174496 02/06/08 07:38 AM
Joined: Mar 2005
Posts: 1,213
S
SteveFehr Offline
Member
As a HO as well, I'd say it's preferable to have the fan on a separate switch. Switch with a timer is best.

Re: Bathroom exhaust fans [Re: SteveFehr] #174501 02/06/08 09:09 AM
Joined: Apr 2002
Posts: 7,261
HotLine1 Offline
Member
HCE:
Design issue. Most commercial have fan on with lighting, and some local Health Depts require it, but I have no substantiation for that.



John
Re: Bathroom exhaust fans [Re: HotLine1] #174504 02/06/08 11:18 AM
Joined: Dec 2000
Posts: 4,287
electure Offline
Member
Hotline,

Out here in CA all commercial and industrial occupancies require the fan to be switched with the lights.

Either that or the fan must run continuously, or be on a timer so that the fan is on during business hours.

Of course, I don't have a substantiation for it either laugh

Re: Bathroom exhaust fans [Re: HotLine1] #174505 02/06/08 11:23 AM
Joined: Sep 2005
Posts: 421
togol Offline
Member
I was wondering if anyone has ever considered using a humidistat for the fan in place of switches or timers .

it makes it hands-free and 120v units are available, could even remote a sensor and drive the fan with a relay and xfmr


Tom
Re: Bathroom exhaust fans [Re: togol] #174510 02/06/08 12:43 PM
Joined: Mar 2005
Posts: 1,213
S
SteveFehr Offline
Member
For residences, IRC 2006, M1507.3 requires a bathroom or toilet room to have "Mechanical exhaust capacity of 50cfm intermittent or 20cfm continuous." IRC sets no requirement for how this is implemented, only that the capacity must be there. Same switch, separate switch, humidistat, timer, etc- all OK by IRC.

Commercial is different. IMC 2006 400.3 requires commercial bathrooms in dorms, hotels, etc, to have 35cfm ventilation/person. (Continuous is implied.) As 0 people are in the bathroom when the lights are off and 0cfm required, the fan can be tied into the light switch. I'm not familiar enough with IMC to know any other subtleties of the code, or what specifically applies to restrooms in stores or offices.

Re: Bathroom exhaust fans [Re: SteveFehr] #174513 02/06/08 01:12 PM
Joined: Jun 2007
Posts: 301
J
JValdes Offline
Member
I always seperate fan and light, unless HO wants both together. No violation of NEC in residential.
I used spring timers when my daughters (4) were still at home. Now, we just use regular swiches so we do not have to listen to the fan until it times out.

Re: Bathroom exhaust fans [Re: JValdes] #174525 02/06/08 08:26 PM
Joined: Jan 2008
Posts: 21
J
JoeyD Offline
Member
I was told in MA the building code states the fan has to come on with the light if there is no windows in the bathroom.
I seperate then unless the owner wants them on at the same time. In a half bath I like the fan on with the lights and using panasonic you can't hear them anyways

Re: Bathroom exhaust fans [Re: JoeyD] #174527 02/06/08 09:51 PM
Joined: Apr 2002
Posts: 7,261
HotLine1 Offline
Member
Electure:
Yes, I agree. Comm is on w/lights, or TC control for occupied hrs. I can't place a Article thou, and say it's a design thing.


John

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sbi
sbi
indiana
Posts: 47
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 18
Admin 10
Popular Topics(Views)
279,049 Are you busy
212,153 Re: Forum
199,180 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3