Doug,
In that last link, it looks like the requirement is in a design spec and not the code or a standard. Is it common to see the main breaker or line side in a separate compartment?
yes.
Doug, you think thats bad, consider ULC S524 which is about 60 pages and costs 150.00 from ULC and is required document for installation of fire alarm systems. I dont know how these prices are justified.
The construction of panelboards is part 2 code and the part 2 code fills a library. It is cumulatively all the standards for products. Doug has pointed out C22.2 #29 for panelboards Appendix A lists much of the part 2 publications for electrical products. It is just a listing of publications and 15 pages long or around 750 product standards. This is why inspectors don't enforce part 2. They would need a van to carry their code books. It is much easier to look for an approval sticker.
Panelboards used for a service entry must have the incoming lines separated from the branch section. It serves to barrier those unprotected Hydro conductors from prying fingers. It also give you a chance to shut the buss off when working in the panel.
In BC there is a directive that requires main breakers (combo panels) when located in a branch circuit position to have a barrier over the line terminals as an added safety feature.
When a panel is used as a service entry only service conductors Line, neutral, and ground may be in the main breaker section and the panel must be approved for use as service equipment. When a combination panel is used as a sub panel then branch wiring may pass through the main breaker section as long as the barrier cannot damage the branch wires as they go past.