Joined: Sep 2006
Posts: 155
C
Member
I am trying to find whether or not in the code if I can tap off a 30amp 240v receptacle for a portable space heater in a commercial space onto an existing 60 amp circuit. This is in a large pottery studio, and this is for seasonal heating in berkeley california, and it would not be used at the same time as the kiln that the circuit supplies....but I could not find any ref. about multi outlet appl. circuits and ocp in 2005 nec? Chris

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Jul 2004
Posts: 9,677
Likes: 9
G
Member
Table 210.21(B)(3)


Greg Fretwell
Joined: May 2007
Posts: 47
B
Member
I am trying to find whether or not in the code if I can tap off a 30amp 240v receptacle for a portable space heater in a commercial space onto an existing 60 amp circuit.

If you change the breaker to a 30A wink

crs you ever get anyone to wire your Mom's house?


Design-Build isn't supposed to mean design *as* you build.
Joined: Nov 2007
Posts: 763
K
Member
Also, don’t forget that since this is a branch circuit and not a feeder, the length of the #10 tap conductors would be limited to 18-inches by 210.19[A][4][c]. smile

Joined: Nov 2007
Posts: 763
K
Member
I should clarify that that the #10 taps will only work if you hardwire the heater. tired
Since you want add an additional receptacle, it must be the same rating as the branch circuit.

Joined: Jul 2007
Posts: 1,335
S
Member
The closets thing you can do and meet code is install a small subpanel then install 30 and 60 amp breaker. The hassel may not be worth it because of the clearence requirements for the panel.


"Live Awesome!" - Kevin Carosa
Joined: Jul 2004
Posts: 9,677
Likes: 9
G
Member
You could also "tap" over to a water heater/HVAC type disconnect with a 30a OC device.


Greg Fretwell

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 362
Joined: April 2003
Top Posters(30 Days)
grich 1
Popular Topics(Views)
288,108 Are you busy
220,213 Re: Forum
206,192 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5