0 members (), 591 guests, and 9 robots.
Article 760.8 requires that fire alarm cables and conductors be supported by the building structure. I would like to hear what others think regarding supporting the fire alarm cables from the suspended ceiling support wires. Tony
Workgear for Electricians
Ceiling support wire is not to support nothing but the ceiling
Guys- take a look at NFPA 70 - '05 Edition and check at 300.11(A)(1) & (2) and note that in some cases wiring methods are permitted to be supported by the same support wires that support the ceiling. Now- depending on your definition of "exposed" you might be able to support the cable via the support wires for the ceiling. It would be handy especially if the structural ceiling was 10 feet above the suspended one. I for one would feel comfortable if the suspended ceiling did not have removable panels. If the suspended ceiling had removable panels, my understanding is that this is considered exposed wiring and subject to physical damage due to "normal building use" 760.8. So Tony, "Write it"
George Little
The original posts asked if the support wires for a hanging ceiling can support the FA cable. If the hanger wires are there to support the ceiling the those wires can not be used. A drop ceiling is not considered part of a building structure.
Fl IAEI had a long discussion about this around 1996? when this first showed up in the code. They decided if there were extra wires, beyond what held the ceiling up, you could use these supplemental wires for support. Then the question became, which wires were holding up the ceiling and which ones were extras for wiring method support. They decided common sense would prevail and you should be able to spot the pattern the ceiling guys used and identify the extras.
No, The way I read it.
760.8 refers to surface applications and 300.4.D. Ok.
Now go to 300.11 (A) (1) &(2).
There's the answer.
Additionaly, you must determine what type of wire/conduit you are useing
The more I read this thread, the more I learn about fire alarm wiring above drop ceilings. I've decided that it can be there and would not have to be fastened directly to the structural ceiling but could be on hangers or similar fittings and when this is the case, one would have to look at 300.11 (A) (1) & (2). I said this previously and was echoed by Leland but there is an additional concern in 760.7 that need to be heeded.
George Little
When working in the Chapter 7 Articles you have to look for this statement:
760.3 Other Articles
Circuits and equipment shall comply with 760.3(A) through 760.3(F). Only those sections of Article 300 referenced in this article shall apply to fire alarm systems.
In this case 300.11 is referenced in 760.25 and 760.52(B)so the 300.11 does apply.
As far as 760.7 it doesn't say what the CMP intended. They were trying to prevent you from just laying the cable on top of the ceiling, but the section wording does not really do that. The wording only says you can't prevent the removal of the ceiling tiles. A few fire alarm or any other type of cables would not prevent the removal of the tile. The section should just say that the cables cannot be supported by the tiles or the grid, but it doesn't so now it is a subjective rule as to how many cables can be placed on the tile before it becomes impossible to remove.
Don
Thanks Don, I missed that and it's a good solid reference to wiring above drop ceilings.
Lets have a good 2008. Things have been kinda rough here in Michigan and we need to turn it around.
George Little