hot tub #171496 11/29/07 12:05 PM
Joined: Mar 2005
Posts: 236
watersparkfalls Offline OP
Member
disco within sight refers to commercial installs if memory serves.
i want to put a residential disco around the corner of the house, which clearly it wont be anywhere near "in sight"
it will be a cleaner install with less pipe on the outside(retro/remodel) of the house and more in the dirt.
sound complient?
thanks,
H2O

2017 / 2014 NEC & Related Books and Study Guides
Re: hot tub [Re: watersparkfalls] #171498 11/29/07 12:49 PM
Joined: Jul 2004
Posts: 9,568
G
gfretwell Offline
Member
Commercial spas and hot tubs require an emergency stop. That is separate and different than the disconnect within site of motors which is required in residential too


Greg Fretwell
Re: hot tub [Re: gfretwell] #171586 12/01/07 10:51 AM
Joined: Sep 2007
Posts: 14
D
drum Offline
Member
The few residential hot tubs I have wired I used a spa disconnect which has the GFCI breaker inside it. I installed it futher than 5ft but within site of the tub. After looking at 680.41 I am a bit confused. It says this requirement shall not apply to single family dwellings???? Does this mean the GFCI breaker could go in the main panel and pipe right out to the tub? Maybe a emergency switch for Spa's and Hot Tubs is somthing different???

Re: hot tub [Re: drum] #171591 12/01/07 12:19 PM
Joined: Jul 2004
Posts: 9,568
G
gfretwell Offline
Member
The emergency stop is for the user or rescuer. The disconnect is for service personel. Different things.
The disconnect removes all power, the emergency stop only needs to stop the motors. It is possible to make this one switch but that is not usually how commercial systems work. If nothing else, the emergency stop usually leaves the light on. I have seen some old systems that only turned off the jet pump (the low speed circulation pump and heat kept running) but that is not really legal.


Greg Fretwell
Re: hot tub [Re: gfretwell] #171609 12/01/07 08:31 PM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline
Member
The code reference for the Maintenance Disconnect is 680.12 and this Disconnect must be within sight (you can see it and it's not more than 50 feet away) and it needs to disconnect everything except the lighting. It is not required to be located more than 5 feet from the tub if it is located under the skirt of the tub and not accessible from the persons in the tub. This was hotly discussed at an IAEI seminar in Michigan with Mike Johnston making the statement about the use of the disconnect under the skirt of the tub as being code compliant.


George Little
Re: hot tub [Re: George Little] #171612 12/01/07 09:37 PM
Joined: Sep 2007
Posts: 14
D
drum Offline
Member
Thanks for pointing out 680.12 George
I appriciate everyones help

Re: hot tub [Re: George Little] #171619 12/02/07 02:03 AM
Joined: Feb 2003
Posts: 939
F
frenchelectrican Offline
Member
Originally Posted by George Little
The code reference for the Maintenance Disconnect is 680.12 and this Disconnect must be within sight (you can see it and it's not more than 50 feet away) and it needs to disconnect everything except the lighting. It is not required to be located more than 5 feet from the tub if it is located under the skirt of the tub and not accessible from the persons in the tub. This was hotly discussed at an IAEI seminar in Michigan with Mike Johnston making the statement about the use of the disconnect under the skirt of the tub as being code compliant.


I am suprised with that what Mike Johnston did say that IMO i dont like the idea have the disconnect under the skirting becase some of the skirting have screw in panel and need screw driver to take it off.

i rather have it exteral location so i can turn it off before i can open the tub panel.

Merci, Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,352 Are you busy
209,224 Re: Forum
196,526 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3