#171496 11/29/07 12:05 PM
Joined: Mar 2005
Posts: 240
Member
disco within sight refers to commercial installs if memory serves.
i want to put a residential disco around the corner of the house, which clearly it wont be anywhere near "in sight"
it will be a cleaner install with less pipe on the outside(retro/remodel) of the house and more in the dirt.
sound complient?
thanks,
H2O

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

watersparkfalls #171498 11/29/07 12:49 PM
Joined: Jul 2004
Posts: 9,770
Likes: 13
G
Member
Commercial spas and hot tubs require an emergency stop. That is separate and different than the disconnect within site of motors which is required in residential too


Greg Fretwell
gfretwell #171586 12/01/07 10:51 AM
Joined: Sep 2007
Posts: 14
D
Member
The few residential hot tubs I have wired I used a spa disconnect which has the GFCI breaker inside it. I installed it futher than 5ft but within site of the tub. After looking at 680.41 I am a bit confused. It says this requirement shall not apply to single family dwellings???? Does this mean the GFCI breaker could go in the main panel and pipe right out to the tub? Maybe a emergency switch for Spa's and Hot Tubs is somthing different???

drum #171591 12/01/07 12:19 PM
Joined: Jul 2004
Posts: 9,770
Likes: 13
G
Member
The emergency stop is for the user or rescuer. The disconnect is for service personel. Different things.
The disconnect removes all power, the emergency stop only needs to stop the motors. It is possible to make this one switch but that is not usually how commercial systems work. If nothing else, the emergency stop usually leaves the light on. I have seen some old systems that only turned off the jet pump (the low speed circulation pump and heat kept running) but that is not really legal.


Greg Fretwell
gfretwell #171609 12/01/07 08:31 PM
Joined: Jan 2004
Posts: 1,507
G
Member
The code reference for the Maintenance Disconnect is 680.12 and this Disconnect must be within sight (you can see it and it's not more than 50 feet away) and it needs to disconnect everything except the lighting. It is not required to be located more than 5 feet from the tub if it is located under the skirt of the tub and not accessible from the persons in the tub. This was hotly discussed at an IAEI seminar in Michigan with Mike Johnston making the statement about the use of the disconnect under the skirt of the tub as being code compliant.


George Little
George Little #171612 12/01/07 09:37 PM
Joined: Sep 2007
Posts: 14
D
Member
Thanks for pointing out 680.12 George
I appriciate everyones help

George Little #171619 12/02/07 02:03 AM
Joined: Feb 2003
Posts: 939
F
Member
Originally Posted by George Little
The code reference for the Maintenance Disconnect is 680.12 and this Disconnect must be within sight (you can see it and it's not more than 50 feet away) and it needs to disconnect everything except the lighting. It is not required to be located more than 5 feet from the tub if it is located under the skirt of the tub and not accessible from the persons in the tub. This was hotly discussed at an IAEI seminar in Michigan with Mike Johnston making the statement about the use of the disconnect under the skirt of the tub as being code compliant.


I am suprised with that what Mike Johnston did say that IMO i dont like the idea have the disconnect under the skirting becase some of the skirting have screw in panel and need screw driver to take it off.

i rather have it exteral location so i can turn it off before i can open the tub panel.

Merci, Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Niko
Niko
Campbell, CA
Posts: 356
Joined: August 2006
Top Posters(30 Days)
Trumpy 7
NORCAL 5
Popular Topics(Views)
300,341 Are you busy
230,001 Re: Forum
214,810 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5