Generac Generator Wiring #171075 11/19/07 06:59 AM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline OP
Member
Does anyone have a comment on the wiring method used to connect the battery charger and interlock wiring between the generator and the transfer switch? Let me explain- The transfer switch (200a. Service rated) is located about 100 feet the generator. The transfer switch has overcurrent protection integral with the switch. There is a 240v. fuse block located within the transfer switch and this is used to supply the battery charger located in the generator enclousure. There is a 24v. circuit between the generator and the transfer switch used to trigger a relay an hence the transfer of power. I think the 24v. power source is in the generator. I say "I think" because I have not been able to get much information from Generac. So my question is: What wiring method would I expect to see for this installation? The installation in question has a run of SER for the load and CL2 18/4 for the 240v. battery charger circuit and the 24v. interlock circuit.
I believe the CL2 would be suitable for the relay interlock wiring if the circuit were Class 2 but I think the 240v. circuit would require an equipment grounding conductor and should not be wired with CL2 cable. I apologize for the length of this post but Hey! you want details don't you?


George Little
2017 / 2014 NEC & Related Books and Study Guides
Re: Generac Generator Wiring [Re: George Little] #171083 11/19/07 11:41 AM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Offline
Member
CL2 is only good for class 2 725 circuits if I read 725.61 right. If this comes from a listed class 2 supply (<30v limited current) and the cable is isolated from line voltage conductors I would say it was OK. Otherwise I think I would want to see an article 725 class 1 wiring method, which looks substantially like chapter 3 wiring methods.


Greg Fretwell
Re: Generac Generator Wiring [Re: gfretwell] #171090 11/19/07 03:37 PM
Joined: Dec 2003
Posts: 751
E
earlydean Offline
Member
725.52 allows Class 2 or 3 circuits to be installed as Class 1 circuit IN THEIR ENTIRETY. Which would also allow them to be in the same enclosure as line voltage.


Earl
Re: Generac Generator Wiring [Re: earlydean] #171102 11/19/07 09:03 PM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline OP
Member
Dean- I saw that and I would have no problem with it if the installation were not installed using CL2 cable run along side the SER cable This would not give me the wiring method of Chapter 3. I would say NM cable or any of the metal jacketed cables or EMT would be compliant. Also, unless I'm mistaken, I would need a grounding conductor.

Part of the problem is the Classification of the circuits. The manufacturer is very difficult when it comes to supplying information.

Last edited by George Little; 11/19/07 09:05 PM.

George Little

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,645 Are you busy
209,569 Re: Forum
196,923 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3