I know the depth under cement is normally 4 " with RNC, but just wondering if the depth could be the same with paving stones? The job I'm on is having pavers put down around their pool ( proffesionally ) with gravel etc. and the installer said you would have to drill the pavers out. As far as I know the code don't specify this as an option, but what do you think an inspector might say about this?? I'll probably go the 12" rule for circuits that are GFI protected and rated 20 amps or less, but in this case it would be NICE to have it the same as concrete. I hate to bug the inspectors any more than I have to. I've called on them quiet a bit lately. Thanks, Steve
|
|
|
|
Joined: Jul 2004
Posts: 9,934 Likes: 34
Member
|
300.5 uses the words "concrete" and "slab". That can't be confused with pavers. I won't say your AHJ won't go along but I am not sure how. RNC is only 6" anyway so he might consider 2" of paver as being part of the 6" cover. Keep it 5' away from the water if at all possible.
Greg Fretwell
|
|
|
|
Joined: Oct 2002
Posts: 482
Member
|
I agree with Greg on 300.5, as concrete is more of a continuious material, and more "permenant" in a sense.
However, I have SEEN RNC laid to about 6" below paver bottoms and also have seen it pass inspection. As far as "drilling out" the pavers, I'd have to question the logic in this, if I'm getting what you mean.
If acheiving a 12" depth is an issue, you might have to bite the bullet and inquire with the AHJ as to how he inturprets 300.5. A screw up here could cause a re-do, and nobody wants to work for free!
Good Luck!
|
|
|
|
Joined: Jul 2004
Posts: 9,934 Likes: 34
Member
|
Using RNC I am not sure when it ever needs to be more than 6" down if you aren't going under a road, runway or parking lot. Look at 680.10 for a more specific answer. You still see 6" and I could see how an AHJ might measure from the top of the paver.
Greg Fretwell
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
Greg- You guys are talking about RNC not RMC Double check your comments. (I think)
George Little
|
|
|
|
Joined: Jul 2004
Posts: 9,934 Likes: 34
Member
|
I typed it several times and still never realized we weren't talking about "rigid". Sorry for the confusion. I guess that is why I used to always say RNMC for the plastic.
Greg Fretwell
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
I'll let it slide this time Greg but only this time
George Little
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 3
Cat Servant Member
|
I really hate to sound like a broken record .... but does not Section 90 of the NEC plainly state "this is not a design manual?"
So, how deep should the pipe be buried? Well, as deep as it needs to be when it exits from the protection of the slab, would be a good start. Or, do you plan on changing the trench depth every time you have a change of the surface material? Lots of luck sanding the angled parts.
Or, consider this: what's a likely cause for the pipe being damaged? Besides the gardener using his shovel to look for irrigation lines ... how about frost heave? I don't care how well the pavers are laid .... give them a few frost cycles, and they'll be all over the place. Maybe the angled pavers will now even act like scissors on your pipe.
Whatever depth you decide upon, make it an honest depth. That is, to the top of the pipe, after it's properly bedded in sand - and NOT the rough depth of the trench! This means a 6" burial depth starts off with a 12" ditch.
|
|
|
Tom