Hospital Transfer switch and Panels Em system under 150 KVA.
Critical System = Seperate panel, Seperate Conduits and wire.
No mixing with other systems.
Lifesafety system = Same
Equipment System = Same
At no time can theses three systems share and panels or raceways of the others.(expect as noted in 517-30 c (1)
Opinions Please

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: May 2002
Posts: 1,716
R
Member
Ernie, this is true.

There should be no problem in compliance if the job is planned.

The three Essential system branches are pretty much aligned with articles 700, 701, and 702 if you think about it.

Roger

Joined: Mar 2005
Posts: 1,213
S
Member
The equipment system can share raceways, etc, with nonessential loads. Critical and life safety must be segretated, though.