On a residential service calculation, can the main breaker be calculated at 100% or does it have to be 80%?, code ref. please.


2017 / 2014 NEC & Related Books and Study Guides
Joined: Nov 2004
Posts: 14
S
Member

The reason I ask about the main, is because I'm installing a hot tub that has dual ratings, 30 amp and 50 amp circuit. The service size is 150 Amps, with a electric range, dryer and AC for major appliances. If I do a service calculation with the added hot tub load, I get 120 amps with the 30 amp hot tub load and 132 amp with the 50 amp hot tub load, so by using the service calculations, can I put the hot tub on the 50 amp circuit or does it have to go on the 30 amp circuit?

My inspector is telling me that the calculated load can't be more than 80 % of the main breaker, 120 Amps.

I see in the code book, on page 718 example D2c that the calculated load is 144.96 with a service
size of 150 amp.

I believe that I can add to this service as long as my service calculation are 150 amp or less.


Thanks George


Last edited by Sparky_1; 10/21/07 10:42 PM.
Joined: Jan 2004
Posts: 1,507
G
Member
And the answer is 100% The code references are: 230.42, 215.2, 210.19
The issue is "continuous load". Since residential loads are not considered to be continuous you can load a branch circit, feeder or Service to it's actual rating which is 100%. I don't think it's a good idea but the code allows it. Most inspectors would recommend a little head room and most contractors agree and provide this head room.


George Little
Joined: Jul 2004
Posts: 9,669
Likes: 6
G
Member
Dwelling loads better be "diverse" or we will have to repeal 310.15(B)(6) wink


Greg Fretwell

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
lil suzi
lil suzi
Midwest
Posts: 57
Joined: August 2003
Top Posters(30 Days)
dsk 7
Popular Topics(Views)
284,885 Are you busy
217,432 Re: Forum
203,744 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5