Euro fase low voltage recessed #168425
09/04/07 07:41 AM
09/04/07 07:41 AM
J
jkraft  Offline OP
Member
Joined: May 2003
Posts: 74
I'm having a problem with these cabinet lights. There's 5 of them with 20 watt MR11+C lamps connected to a 150W/12V electronic transformer, that keeps cycling off and on. The lights are about 20' away from the xfmr fed with 16/4 speaker wire used in parallel.

As a comparison I connected 4 of the 20W lamps directly to a Malibu 200W/12V landscape xfmr. The xfmr gets very hot and the lamps are burning out.

Anyone have experience with this?

Work Gear for Electricians and the Trades
Re: Euro fase low voltage recessed [Re: jkraft] #168427
09/04/07 08:08 AM
09/04/07 08:08 AM
Z
Zapped  Offline
Member
Joined: Oct 2002
Posts: 482
Huntington Beach, CA, USA
Have you tried putting a meter on the xfmr? Try measuring Voltage and Amps on the secondary side, both under load and disconnected from load. This will probably tell you everything you need to know. Also check the line side voltage under both conditions to see if there is any problem there.

Without benefit of these measurements, my first guess is a bad xfmr, unless there is a dimmer on the circuit. They have dimmers made specifically for LV lighting because standard dimmers don't always work properly with transformers, especially electronic transfromers.

Good Luck!

Re: Euro fase low voltage recessed [Re: Zapped] #168429
09/04/07 01:05 PM
09/04/07 01:05 PM
G
geoff in UK  Offline
Member
Joined: Dec 2002
Posts: 194
UK
I agree, but suggest not a digital meter, or at least use one that measures RMS; You may be dealing with odd waveforms.
Also, I think under no load condition many electronic transformers will shut down and show no output.
(Are you sure they are 20 watt lamps ?)

Re: Euro fase low voltage recessed [Re: geoff in UK] #168431
09/04/07 01:27 PM
09/04/07 01:27 PM
J
jkraft  Offline OP
Member
Joined: May 2003
Posts: 74
Originally Posted by geoff in UK
I agree, but suggest not a digital meter, or at least use one that measures RMS; You may be dealing with odd waveforms.
Also, I think under no load condition many electronic transformers will shut down and show no output.
(Are you sure they are 20 watt lamps ?)


Yep they are 20 watts, and you are correct the electronic transformer shows 0 volts on my digital meter. Should I try my old analog meter?

Re: Euro fase low voltage recessed [Re: jkraft] #168441
09/04/07 09:05 PM
09/04/07 09:05 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,323
Estero,Fl,usa
Put one light on the transformer for a load and measure that.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044