445.18 Disconnect at Generator location & type #167486 08/13/07 07:54 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
445.18 requires a disconnect at the Generator location. I read this to be a Fused or Breaker type . 240.21 Conductors must be protected at the point where they receive there supply. I feel the disconnect also should be close to the generator location. .other Opnions please??

2017 / 2014 NEC & Related Books and Study Guides
Re: 445.18 Disconnect at Generator location & type [Re: Yoopersup] #167490 08/13/07 09:30 PM
Joined: Jul 2007
Posts: 265
W
wire_twister Offline
Member
We sometimes put in generators for cell phone equipment, most are Generac sets. These have breakers on the gen-set where the conductors hook to the set, not what I consider accesseble though, they are inside the gen-set cabinet which is usualy locked.


Jimmy

Life is tough, Life is tougher when you are stupid
Re: 445.18 Disconnect at Generator location & type [Re: wire_twister] #167575 08/15/07 06:23 PM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline
Member
Be cafeful Jimmy by using the breaker that comes with the equipment. It may be considers as supplemental OCP thus does not meet protection requirements. It should state in the lititerture that come with the genset. I am not familar with Generac so you may be right and I may be wrong. The paperwork that come with out to tell you what size of diconnect to install. Also do not be a retard like my self who put the genset leads on the bottom lugs. The genset is the line not the load.


"Live Awesome!" - Kevin Carosa
Re: 445.18 Disconnect at Generator location & type [Re: sparkyinak] #167578 08/15/07 06:57 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
This is a very large Generator and came from the factory without a disconnect on it. Thus the question.Owner wants to install the disconnect same room aprox. 40-70 ft away,

Re: 445.18 Disconnect at Generator location & type [Re: Yoopersup] #167581 08/15/07 08:39 PM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline
Member
Closer the better, in sight of not to exceed 50 feet.


"Live Awesome!" - Kevin Carosa
Re: 445.18 Disconnect at Generator location & type [Re: sparkyinak] #167591 08/16/07 12:56 AM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Online Content
Member
How do you protect the conductors and the generator from a fault in that 50 feet? Are we assuming a short would stall the generator?


Greg Fretwell
Re: 445.18 Disconnect at Generator location & type [Re: gfretwell] #167610 08/16/07 10:16 AM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline
Member
The disconnect needs to be close as practical not to exceed 50 feet. The 50 foot rule is somtimes it is not safe to be right at the equipment or if the equipment is elevated


"Live Awesome!" - Kevin Carosa
Re: 445.18 Disconnect at Generator location & type [Re: sparkyinak] #167699 08/17/07 09:30 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
Show me the Code sections ? 50ft and within sight is in mtrs .This Generator is 13.8 volts .

Re: 445.18 Disconnect at Generator location & type [Re: Yoopersup] #167702 08/17/07 10:33 PM
Joined: Feb 2003
Posts: 939
F
frenchelectrican Offline
Member
Originally Posted by Yoopersup
Show me the Code sections ? 50ft and within sight is in mtrs .This Generator is 13.8 volts .


if i am reading this right this is a low voltage or high votlage ??

13.8 volts or 13.8 KV ??

if it is 13.8 KV there is few other rules will show up with this type of voltage i am not too sure where it land but part of it will be not in the NEC

Merci , Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Re: 445.18 Disconnect at Generator location & type [Re: frenchelectrican] #167707 08/18/07 08:24 AM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
It is 13.8 KV and Yes it is part of the NEC as its in a hospital not utilty owned.

Page 1 of 3 1 2 3

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,689 Are you busy
209,610 Re: Forum
196,959 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3