ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Childrens safety outlets
by dsk - 06/25/22 04:07 PM
AC-DC stage Ultra-Fast charger, how it's made?
by libellis - 06/25/22 12:17 PM
Your favourite food?
by NORCAL - 06/16/22 12:06 AM
Price action trading with RENKO
by gfretwell - 06/15/22 02:08 PM
Please Help Wiring DCDC Buck Converter
by gfretwell - 06/15/22 01:58 PM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
0 members (), 47 guests, and 21 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 3 1 2 3
Joined: Mar 2003
Posts: 849
Y
Member
445.18 requires a disconnect at the Generator location. I read this to be a Fused or Breaker type . 240.21 Conductors must be protected at the point where they receive there supply. I feel the disconnect also should be close to the generator location. .other Opnions please??

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Jul 2007
Posts: 265
W
Member
We sometimes put in generators for cell phone equipment, most are Generac sets. These have breakers on the gen-set where the conductors hook to the set, not what I consider accesseble though, they are inside the gen-set cabinet which is usualy locked.


Jimmy

Life is tough, Life is tougher when you are stupid
Joined: Jul 2007
Posts: 1,335
S
Member
Be cafeful Jimmy by using the breaker that comes with the equipment. It may be considers as supplemental OCP thus does not meet protection requirements. It should state in the lititerture that come with the genset. I am not familar with Generac so you may be right and I may be wrong. The paperwork that come with out to tell you what size of diconnect to install. Also do not be a retard like my self who put the genset leads on the bottom lugs. The genset is the line not the load.


"Live Awesome!" - Kevin Carosa
Joined: Mar 2003
Posts: 849
Y
Member
This is a very large Generator and came from the factory without a disconnect on it. Thus the question.Owner wants to install the disconnect same room aprox. 40-70 ft away,

Joined: Jul 2007
Posts: 1,335
S
Member
Closer the better, in sight of not to exceed 50 feet.


"Live Awesome!" - Kevin Carosa
Joined: Jul 2004
Posts: 9,696
Likes: 11
G
Member
How do you protect the conductors and the generator from a fault in that 50 feet? Are we assuming a short would stall the generator?


Greg Fretwell
Joined: Jul 2007
Posts: 1,335
S
Member
The disconnect needs to be close as practical not to exceed 50 feet. The 50 foot rule is somtimes it is not safe to be right at the equipment or if the equipment is elevated


"Live Awesome!" - Kevin Carosa
Joined: Mar 2003
Posts: 849
Y
Member
Show me the Code sections ? 50ft and within sight is in mtrs .This Generator is 13.8 volts .

Joined: Feb 2003
Posts: 939
F
Member
Originally Posted by Yoopersup
Show me the Code sections ? 50ft and within sight is in mtrs .This Generator is 13.8 volts .


if i am reading this right this is a low voltage or high votlage ??

13.8 volts or 13.8 KV ??

if it is 13.8 KV there is few other rules will show up with this type of voltage i am not too sure where it land but part of it will be not in the NEC

Merci , Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Joined: Mar 2003
Posts: 849
Y
Member
It is 13.8 KV and Yes it is part of the NEC as its in a hospital not utilty owned.

Page 1 of 3 1 2 3

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Top Posters(30 Days)
triple 3
grich 2
dsk 2
Popular Topics(Views)
292,968 Are you busy
224,975 Re: Forum
210,412 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5