I don't know which is worse, the electrical or the cable.
Is this basement going to be finished? Or did they just put the 2X4s in since they ran out of concrete anchors and bolts? Nevermind: Just noticed the top plate.
One more question, is this a Toll Brothers House?
Ian A.
Last edited by Theelectrikid; 07/23/07 11:13 AM.
Is there anyone on board who knows how to fly a plane?
|
|
|
|
Joined: Jun 2006
Posts: 613
Member
|
Branch wiring through the main breaker section is a fail in the great white north electrical code.
|
|
|
|
Joined: Oct 2006
Posts: 745
Member
|
$600K house with only a 200A service? That must be a pretty expensive neighborhood. Has this passed a final inspection yet? I sure don't see anything to secure the cables within 12" of the panel. Neat workmanship is getting to the point where it's non-existent in these parts.
---Ed---
"But the guy at Home Depot said it would work."
|
|
|
|
Joined: Jan 2005
Posts: 5,370 Likes: 1
Cat Servant Member
|
Several of those connectors have more then two cables in them. I am not aware of any such connectors being listed for use with more than two cables. Look like a violation to me.
Sure, the cable look sloppy as they exit the insulation. Yet, I like the neat arrangement of the wires in the panel, and the tags identifying each wire.
One item that concerns me - and there is no way to tell from the picture if such is the case here - is that such homes often have a spa / hot tub / jacuzzi. As I understand these things, Romex (the wiring method used here exclusively) is not allowed for such a circuit, as the ground wire must be both full size, and insulated.
|
|
|
|
Joined: Apr 2005
Posts: 32
Junior Member
|
Off hand 110.12 comes to mind,I am not sure if there is a berating factor for those cables bundled. for $600k I would expect better.
"If your going to be stupid, You gotta be tough"
|
|
|
|
Joined: Apr 2003
Posts: 60
Member
|
The outlet below and to the left of the panel. Am I seeing a single hot wire going through the offset nipple, and two romex coming in from the top? Is the GFI (it appears) wired in series with others, and not fed from this panel? And what is that hot doing without neutral or ground?
|
|
|
|
Joined: Apr 2005
Posts: 200
Member
|
What's with the aluminum wire coming out of the wire clamp? GEC?
Cliff
|
|
|
|
Joined: Dec 2001
Posts: 2,498
Member
|
Let's see... 3 bundled cables... would make rated ampacity x 0.7 in my corner of the world. Not exactly knowing US ampacity tables I'd guess if that's #14 it would make for a lot of 10A and smaller breakers...
|
|
|
|
Joined: Jan 2005
Posts: 5,370 Likes: 1
Cat Servant Member
|
Good catch, Hemingray. While aluminum is technically allowed as a GEC, it can't get within 18" of the ground. Since it's supposed to run without splicing, how it attaches to the ground rod / ufer is anyone's guess.
You need to derate for bundling only if the 'bundle' is over two feet long. I don't think the bundles are long enough for that to be an issue.
As for the receptacle ... I think I see a neutral wire there ... it's just that most of it is out of view, behind the lip of the box.
|
|
|