Emt supports? #165800
07/05/07 08:02 PM
07/05/07 08:02 PM
B
barbwire  Offline OP
Junior Member
Joined: May 2003
Posts: 17
Hello all, I was told that on a vertical EMT pipe run you can support every 30 feet, but I cant find this in the code, is this true? Or does the 10 ft rule still apply?

2017 / 2014 NEC & Related Books and Study Guides
Re: Emt supports? [Re: barbwire] #165801
07/05/07 09:04 PM
07/05/07 09:04 PM
L
Luketrician  Offline
Member
Joined: Jul 2006
Posts: 272
Sale Creek, TN USA
The way I read it, 358.30(A) gives a general statement which covers this.

"EMT shall be securely fastened in place every 3m (10 ft)."

I could not find any other information though, I may be missing something here. There is an exeception to this if you are fishing a wall though.


Luke Clarke
Electrical Planner for TVA.

Re: Emt supports? [Re: Luketrician] #165803
07/05/07 09:38 PM
07/05/07 09:38 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,306
Estero,Fl,usa
Don't forget you also have to support the conductors if these risers get that tall.


Greg Fretwell
Re: Emt supports? [Re: gfretwell] #165860
07/06/07 03:05 PM
07/06/07 03:05 PM
B
barbwire  Offline OP
Junior Member
Joined: May 2003
Posts: 17
Thanks for the responce, I couldn't find anything either, 10 ft it is.

Re: Emt supports? [Re: barbwire] #165903
07/07/07 10:21 AM
07/07/07 10:21 AM
A
Alan Nadon  Offline
Member
Joined: Mar 2005
Posts: 399
Elkhart, IN. USA
Greg mentioned conductor support it is located in section 300.19


Alan--
If it was easy, anyone could do it.
Re: Emt supports? [Re: Alan Nadon] #165904
07/07/07 10:33 AM
07/07/07 10:33 AM
B
barbwire  Offline OP
Junior Member
Joined: May 2003
Posts: 17
Yes, Thank you Guys, I referred to the table in 300.19, Thanks again.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
Popular Topics(Views)
251,660 Are you busy
188,793 Re: Forum
178,511 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 15 (0.004s) Memory: 0.9758 MB (Peak: 1.1251 MB) Zlib enabled. Server Time: 2018-11-21 12:00:48 UTC