Hello all, I was told that on a vertical EMT pipe run you can support every 30 feet, but I cant find this in the code, is this true? Or does the 10 ft rule still apply?
2017 / 2014 NEC & Related Books and Study Guides
barbwire #165801 07/05/07 10:04 PM
The way I read it, 358.30(A) gives a general statement which covers this.
"EMT shall be securely fastened in place every 3m (10 ft)."
I could not find any other information though, I may be missing something here. There is an exeception to this if you are fishing a wall though.
Luke Clarke
Electrical Planner for TVA.
Don't forget you also have to support the conductors if these risers get that tall.
gfretwell #165860 07/06/07 04:05 PM
Thanks for the responce, I couldn't find anything either, 10 ft it is.
barbwire #165903 07/07/07 11:21 AM
Greg mentioned conductor support it is located in section 300.19
Alan--
Yes, Thank you Guys, I referred to the table in 300.19, Thanks again.