3 phase transformer #163236 05/04/07 05:26 PM
Joined: Aug 2005
Posts: 64
K
kyelectric Offline OP
Member
On a 75kva 3 phase transformer I use my Ugly's book to see that it is rated for 180 amps full load current. Looking at the allowable ampacities of conductors table I can see that using 75 C column and going to 180 amps that I can use 4/0 alum. or copper clad cable. When I inspected the transformer I found it to be wired with 4/0 paralled USE type cables. Was that over kill or why did they parallel the cables with 6 line conductors and 2 neutrals instead of using 3 line conductors and 1 neutral. I know it can't hurt to over size the wire (except cost and lug size in the panels). Thanks!

Work Gear for Electricians and the Trades
Re: 3 phase transformer [Re: kyelectric] #163237 05/04/07 05:29 PM
Joined: Dec 2005
Posts: 17
C
codewarrior Offline
Member
They problably did that because of voltage drop to a long distance load.

Re: 3 phase transformer [Re: codewarrior] #163260 05/04/07 10:37 PM
Joined: Aug 2005
Posts: 64
K
kyelectric Offline OP
Member
Codewarrior,
You are correct. I went back by there this afternoon and realized that the run is probably around 250 to 300 feet. So, they upsized to compensate for voltage drop. Thanks for the reply.

Re: 3 phase transformer [Re: kyelectric] #163263 05/04/07 10:49 PM
Joined: Dec 2005
Posts: 17
C
codewarrior Offline
Member
Glad I could be of help grin


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 10
Trumpy 7
Popular Topics(Views)
279,176 Are you busy
212,237 Re: Forum
199,252 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3