3 phase transformer #163236
05/04/07 05:26 PM
05/04/07 05:26 PM
K
kyelectric  Offline OP
Member
Joined: Aug 2005
Posts: 64
On a 75kva 3 phase transformer I use my Ugly's book to see that it is rated for 180 amps full load current. Looking at the allowable ampacities of conductors table I can see that using 75 C column and going to 180 amps that I can use 4/0 alum. or copper clad cable. When I inspected the transformer I found it to be wired with 4/0 paralled USE type cables. Was that over kill or why did they parallel the cables with 6 line conductors and 2 neutrals instead of using 3 line conductors and 1 neutral. I know it can't hurt to over size the wire (except cost and lug size in the panels). Thanks!

Work Gear for Electricians and the Trades
Re: 3 phase transformer [Re: kyelectric] #163237
05/04/07 05:29 PM
05/04/07 05:29 PM
C
codewarrior  Offline
Member
Joined: Dec 2005
Posts: 17
Camden,New Jersey
They problably did that because of voltage drop to a long distance load.

Re: 3 phase transformer [Re: codewarrior] #163260
05/04/07 10:37 PM
05/04/07 10:37 PM
K
kyelectric  Offline OP
Member
Joined: Aug 2005
Posts: 64
Codewarrior,
You are correct. I went back by there this afternoon and realized that the run is probably around 250 to 300 feet. So, they upsized to compensate for voltage drop. Thanks for the reply.

Re: 3 phase transformer [Re: kyelectric] #163263
05/04/07 10:49 PM
05/04/07 10:49 PM
C
codewarrior  Offline
Member
Joined: Dec 2005
Posts: 17
Camden,New Jersey
Glad I could be of help grin


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles, CA
Posts: 349
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Popular Topics(Views)
249,478 Are you busy
187,395 Re: Forum
176,739 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 15 (0.004s) Memory: 0.9589 MB (Peak: 1.0897 MB) Zlib enabled. Server Time: 2018-09-26 14:41:31 UTC