#163236 05/04/07 04:26 PM
Joined: Aug 2005
Posts: 64
K
Member
On a 75kva 3 phase transformer I use my Ugly's book to see that it is rated for 180 amps full load current. Looking at the allowable ampacities of conductors table I can see that using 75 C column and going to 180 amps that I can use 4/0 alum. or copper clad cable. When I inspected the transformer I found it to be wired with 4/0 paralled USE type cables. Was that over kill or why did they parallel the cables with 6 line conductors and 2 neutrals instead of using 3 line conductors and 1 neutral. I know it can't hurt to over size the wire (except cost and lug size in the panels). Thanks!

Joined: Dec 2005
Posts: 17
C
Member
They problably did that because of voltage drop to a long distance load.

Joined: Aug 2005
Posts: 64
K
Member
Codewarrior,
You are correct. I went back by there this afternoon and realized that the run is probably around 250 to 300 feet. So, they upsized to compensate for voltage drop. Thanks for the reply.

Joined: Dec 2005
Posts: 17
C
Member
Glad I could be of help grin


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31
Joined: December 2011
Top Posters(30 Days)
triple 2
Popular Topics(Views)
303,305 Are you busy
232,258 Re: Forum
217,018 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5