The scenario: My sisters new lake house needs to have its dock mounted power pedestal placed/connected. The brother (me) was asked to do this simple project. The previous home owner had given them his complete set-up for this. There is a pedestal mounted disconnect with 240 30 amp plug-in point at shoreline - 100 feet of SO cord with twist-locks for connecting between the marine grade dock power pedestal and shoreline power. I understand you cant protect this whole thing with GFI protection without nuisance tripping. I simply don't feel comfortable running 100 feet of SO cord zip tied (suggested method) for 100' along a dock. They have a 4 year old daughter who is very inquisitive... I want to say sorry I dont feel comfortable connecting this but, I know the handyman will be next in line to do it.
Any suggestions? Money is not an issue with them. I was thinking (if I do it) that I could possibly protect the SO cord with PVC along the dock without gluing it so the whole thing could be dis-assembled before dock removal in the fall.

Thanks John

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

Joined: May 2005
Posts: 984
Likes: 2
G
Member
Mount some lengths of PVC, not connected together, as a route for the SO cord.
That way you can run the cord through the pipe and most of it will be concealed from the view of the kiddie.
You're not using the PVC as a raceway so much as using it as a support for the cord.


Ghost307
ghost307 #162516 04/20/07 02:28 PM
Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
Twin City Sparky:
The east coast way (NJ) is to 'hang' the SO at the side of the dock, with 'slack'. As it is out of site, it should be OK. I've seen PVC cable hooks screwed to the beams, the cable laid-in and done. BTW, not a lake, but bay, river, & lagoon tidal waters.

John


John
HotLine1 #162549 04/21/07 01:39 AM
Joined: Jul 2004
Posts: 10,048
Likes: 38
G
Member
I am not sure why you say this can't be GFCI.


Greg Fretwell
Joined: Mar 2006
Posts: 52
T
Member
Portable SO cord has a certain amount of capitance leakeage to ground. I've read that 100ft of SO cord alone can leak the 5 milliamps to ground resulting in a false trip... John

Joined: Jul 2004
Posts: 10,048
Likes: 38
G
Member
I would say if there is that much leakage it is not safe for the application.


Greg Fretwell
gfretwell #162598 04/22/07 05:22 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
With any long run, even with good wire, capacitive coupling between the circuit conductors and the EGC or steel raceway may become an issue.

If it was up to me I would not GFCI protect this feeder to the pedestal. IMHO it is never a good design to GFCI protect a feeder.

I would make sure my ground fault path back to the source was as reliable as I could possibly make it.





Bob Badger
Construction & Maintenance Electrician
Massachusetts
Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

Joined: Mar 2006
Posts: 52
T
Member
No GFI used. I ran PVC along the top outer edge of the dock. replaced all cord ends, checked all connections. Looks nice and safe - sister and hubby are happy! Thanks everyone for the replies.

John

Joined: Jul 2004
Posts: 10,048
Likes: 38
G
Member
This "coupling" BS is just a way to rationalize water in boxes and other real ground faults. If 100' of wire couples enough to trip GFCI I would have them tripping all over my house.


Greg Fretwell
gfretwell #162609 04/22/07 11:54 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Originally Posted by gfretwell
This "coupling" BS is just a way to rationalize water in boxes and other real ground faults.


BS? smirk

Greg it is not BS, it is a real issue.

As a an example when you wire a line isolation monitoring panel you should not even use THHN/THWN at all as its dielectric strength is to low.

Now I fully understand that LIMs are more sensitive to this than a GFCI but the cause and theory are the same.

Now instead of the LIM take a less sensitive class A GFCI and run a couple hundred feet of circuits on the load side of it and you may have a real problem.

If you are interested in some more info read the linked article.

Impedance of Wiring on Hospital Isolated Power Systems used in Operating Rooms

Another example of capacitance coupling can be observed when testing the continuity of long cable runs with a good meter. You will get an ohms reading until the cable (capacitor) charges.


Last edited by iwire; 04/22/07 11:58 AM.

Bob Badger
Construction & Maintenance Electrician
Massachusetts
Page 1 of 2 1 2