Shore Power #162502
04/20/07 11:41 AM
04/20/07 11:41 AM
T
TwinCitySparky  Offline OP
Member
Joined: Mar 2006
Posts: 52
Minnesota
The scenario: My sisters new lake house needs to have its dock mounted power pedestal placed/connected. The brother (me) was asked to do this simple project. The previous home owner had given them his complete set-up for this. There is a pedestal mounted disconnect with 240 30 amp plug-in point at shoreline - 100 feet of SO cord with twist-locks for connecting between the marine grade dock power pedestal and shoreline power. I understand you cant protect this whole thing with GFI protection without nuisance tripping. I simply don't feel comfortable running 100 feet of SO cord zip tied (suggested method) for 100' along a dock. They have a 4 year old daughter who is very inquisitive... I want to say sorry I dont feel comfortable connecting this but, I know the handyman will be next in line to do it.
Any suggestions? Money is not an issue with them. I was thinking (if I do it) that I could possibly protect the SO cord with PVC along the dock without gluing it so the whole thing could be dis-assembled before dock removal in the fall.

Thanks John

Work Gear for Electricians and the Trades
Re: Shore Power [Re: TwinCitySparky] #162515
04/20/07 01:47 PM
04/20/07 01:47 PM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 958
Chicago Illinois USA
Mount some lengths of PVC, not connected together, as a route for the SO cord.
That way you can run the cord through the pipe and most of it will be concealed from the view of the kiddie.
You're not using the PVC as a raceway so much as using it as a support for the cord.


Ghost307
Re: Shore Power [Re: ghost307] #162516
04/20/07 02:28 PM
04/20/07 02:28 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,036
Brick, NJ USA
Twin City Sparky:
The east coast way (NJ) is to 'hang' the SO at the side of the dock, with 'slack'. As it is out of site, it should be OK. I've seen PVC cable hooks screwed to the beams, the cable laid-in and done. BTW, not a lake, but bay, river, & lagoon tidal waters.

John


John
Re: Shore Power [Re: HotLine1] #162549
04/21/07 01:39 AM
04/21/07 01:39 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
I am not sure why you say this can't be GFCI.


Greg Fretwell
Re: Shore Power [Re: TwinCitySparky] #162556
04/21/07 09:15 AM
04/21/07 09:15 AM
T
TwinCitySparky  Offline OP
Member
Joined: Mar 2006
Posts: 52
Minnesota
Portable SO cord has a certain amount of capitance leakeage to ground. I've read that 100ft of SO cord alone can leak the 5 milliamps to ground resulting in a false trip... John

Re: Shore Power [Re: TwinCitySparky] #162592
04/21/07 11:38 PM
04/21/07 11:38 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
I would say if there is that much leakage it is not safe for the application.


Greg Fretwell
Re: Shore Power [Re: gfretwell] #162598
04/22/07 05:22 AM
04/22/07 05:22 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
With any long run, even with good wire, capacitive coupling between the circuit conductors and the EGC or steel raceway may become an issue.

If it was up to me I would not GFCI protect this feeder to the pedestal. IMHO it is never a good design to GFCI protect a feeder.

I would make sure my ground fault path back to the source was as reliable as I could possibly make it.





Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Shore Power [Re: TwinCitySparky] #162603
04/22/07 10:00 AM
04/22/07 10:00 AM
T
TwinCitySparky  Offline OP
Member
Joined: Mar 2006
Posts: 52
Minnesota
No GFI used. I ran PVC along the top outer edge of the dock. replaced all cord ends, checked all connections. Looks nice and safe - sister and hubby are happy! Thanks everyone for the replies.

John

Re: Shore Power [Re: TwinCitySparky] #162607
04/22/07 11:25 AM
04/22/07 11:25 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
This "coupling" BS is just a way to rationalize water in boxes and other real ground faults. If 100' of wire couples enough to trip GFCI I would have them tripping all over my house.


Greg Fretwell
Re: Shore Power [Re: gfretwell] #162609
04/22/07 11:54 AM
04/22/07 11:54 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Originally Posted by gfretwell
This "coupling" BS is just a way to rationalize water in boxes and other real ground faults.


BS? smirk

Greg it is not BS, it is a real issue.

As a an example when you wire a line isolation monitoring panel you should not even use THHN/THWN at all as its dielectric strength is to low.

Now I fully understand that LIMs are more sensitive to this than a GFCI but the cause and theory are the same.

Now instead of the LIM take a less sensitive class A GFCI and run a couple hundred feet of circuits on the load side of it and you may have a real problem.

If you are interested in some more info read the linked article.

Impedance of Wiring on Hospital Isolated Power Systems used in Operating Rooms

Another example of capacitance coupling can be observed when testing the continuity of long cable runs with a good meter. You will get an ohms reading until the cable (capacitor) charges.


Last edited by iwire; 04/22/07 11:58 AM.

Bob Badger
Construction & Maintenance Electrician
Massachusetts
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,641 Are you busy
188,134 Re: Forum
177,810 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.037s Queries: 16 (0.006s) Memory: 1.0273 MB (Peak: 1.2066 MB) Zlib enabled. Server Time: 2018-10-23 03:17:39 UTC