Ok placing service on old house zoned comercial. Did a service 200a metermain.Installed a 60a double pole breaker feeding a main lug 100a panel where the load is nothing 4 rooms no a/c no heat no h20 heater just a storage at feed store. Well the inspector wants exit lights added smokes interconnected.All ok but he has a problem with my feeder to the 100amp main lug panel. Its a 100 amp panel with maybe 20 amp loads I feed with a 60amp and wired based on the 60 a feeder.I need to plead my case why the installation is compliant although he can`t show non compliance.I showed him the load calcs but..... I`d just like to give some code references and such.He`s looking for a 100a main breaker and #3 copper for feeders. If I had a main of 100 I could see his point but still i`d like be able to use code for my point or heck If I`m wrong I`d like to know why by code. Thanks again ps i`m looking also in the code.
|
|
|
|
Joined: Jul 2004
Posts: 9,928 Likes: 34
Member
|
How many square feet? What the the permitted occupancy?
Greg Fretwell
|
|
|
|
Joined: Jun 2005
Posts: 821
Member
|
I'm thinking article 230, the section that requires a minimum 100 AMP service for a dwelling.
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
But it's no longer a dwelling. It's now commercial.
Does the inspector think that because the Main Lug panel is rated @ 100 amps it requires a 100 amp feeder?
|
|
|
|
Joined: May 2005
Posts: 984 Likes: 1
Member
|
I've seen dumber... I ran into an inspector once who looked at a 42 circuit panel full of 20A-1P breakers and asked how I ever expected that to work if I didn't provide a 840A feed to it.
Ghost307
|
|
|
|
Joined: Apr 2002
Posts: 178
OP
Member
|
Just a storage area for a feed store. Actually he`s planning on putting plants and such inside.This was a old old house the wiring was up graded at some point but each room has a pull chain lite and 1 rec.This guy is a fairly new inspector and the town just started there own inspections.He`s now questioned my wire. I ran a 6/3 w/ground from a 60 amp double.
Last edited by Reel-Break; 04/13/07 09:04 AM.
|
|
|
|
Joined: Mar 2005
Posts: 399
Member
|
Look at section 230.79 NEC. If it is a house,i.e. single family dwelling then 100 amps per 230.79 (C) If it is commercial 60 amps per 230.79(D). If you have a permit for the job then have the issuing agency or zoning confirm what the building is for the appropriate electrical connection. Note; Exit signage & lighting is not required in a S.F.D. and smoke detectors are not required in small commercial so the requirements are being applied for both uses. Somebody needs to decide what the building is, either residential or commercial. Alan--
Alan-- If it was easy, anyone could do it.
|
|
|
|
Joined: Jul 2006
Posts: 272
Member
|
Luke Clarke Electrical Planner for TVA.
|
|
|
Posts: 7,381
Joined: April 2002
|
|
|
|
|