Anyone have a drawing for a outdoor fuel tank at a school for their buses.
I installed a shunt trip an e-stop button but unsure how far the e-stop can be from the tank.Also installed rigid pipe with expliosion proof fittings and sealoffs.

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Mar 2007
Posts: 49
A
Member
The Emergency pump shutdown is to be locacated at least 20 feet but less than 100 feet from the dispenseing location. Look at article 514 for more info.

Joined: Nov 2005
Posts: 827
J
Member
I don't know the minimum requirement but that's one thing we don't skimp on. We put them just about anywhere you'll pass on the way out of a problem in the fueling islands and a couple of distant points that you can view them from. We also have a connection to the FACP so that any zone associated with or nearby the fueling will cause an E-Stop on alarm. We can bypass the FACP E-Stop but that will put the FACP into Trouble or Supervisory until enabled. We only use one key reset switch in the Foreman's offices. I sometimes find these reset switches jumpered at which time I tend to light a little fire of my own.
Joe

Joined: Jul 2002
Posts: 680
W
Member
If your trying to meet NEC a shunt trip won't cut it. Doesn't shut off grounded conductor. Is it an unattended operation??


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,158
Joined: May 2003
Top Posters(30 Days)
BigB 3
triple 2
Popular Topics(Views)
305,039 Are you busy
233,457 Re: Forum
218,144 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5