Posted By: johnd24 outdoor gas/diesal tank installation - 04/05/07 09:34 PM
Anyone have a drawing for a outdoor fuel tank at a school for their buses.
I installed a shunt trip an e-stop button but unsure how far the e-stop can be from the tank.Also installed rigid pipe with expliosion proof fittings and sealoffs.
Posted By: ausador Re: outdoor gas/diesal tank installation - 04/06/07 12:39 AM
The Emergency pump shutdown is to be locacated at least 20 feet but less than 100 feet from the dispenseing location. Look at article 514 for more info.
I don't know the minimum requirement but that's one thing we don't skimp on. We put them just about anywhere you'll pass on the way out of a problem in the fueling islands and a couple of distant points that you can view them from. We also have a connection to the FACP so that any zone associated with or nearby the fueling will cause an E-Stop on alarm. We can bypass the FACP E-Stop but that will put the FACP into Trouble or Supervisory until enabled. We only use one key reset switch in the Foreman's offices. I sometimes find these reset switches jumpered at which time I tend to light a little fire of my own.
Joe
Posted By: walrus Re: outdoor gas/diesal tank installation - 04/06/07 12:52 PM
If your trying to meet NEC a shunt trip won't cut it. Doesn't shut off grounded conductor. Is it an unattended operation??