burial depth on pool #161188
03/31/07 10:37 AM
03/31/07 10:37 AM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
If the circuit is GFI protected and not over 20 amps, can I still just go 12" on pool wiring? In the burial depth table in the pool section, it doesn't say anything about it. Thanks Steve...

2017 / 2014 NEC & Related Books and Study Guides
Re: burial depth on pool [Re: sparkync] #161198
03/31/07 11:54 AM
03/31/07 11:54 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,242
Estero,Fl,usa
Everything but the underwater pool light must be 5' away from the pool so the normal rules apply.


Greg Fretwell
Re: burial depth on pool [Re: gfretwell] #161206
03/31/07 12:38 PM
03/31/07 12:38 PM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
Greg, I'm talking on the depth of the trench, not the distance from the pool. In residential, the trench can be minimum of 12" deep if it is GFI protected and not over a 20 amp circuit. I was wondering if that same rule applied on pool wiring, since the chapter on pool wiring has it's on depth table, and it don't say anthing about the 12" rule. Thanks again, Steve....

Re: burial depth on pool [Re: sparkync] #161207
03/31/07 01:09 PM
03/31/07 01:09 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,242
Estero,Fl,usa
You use 680.10 (18" for RNC) but that is not usually a burden since the pool light(s) will usually be the only equipment that is required to be wired inside the 5' zone. This will be >18" deep where it goes into the pool wall so it is not really that hard to keep it 18" for 5 feet. Once you get outside the zone you can ease it up to 12". Since you are pulling a #8 and a SJOW cord you don't want many bends anyway. I don't know any AHJs who think "Where space limitations prevent wiring from being routed a distance 1.5 m (5 ft) or more from the pool ..." refers to anything but wiring supplying pool equipment.


Greg Fretwell
Re: burial depth on pool [Re: gfretwell] #161209
03/31/07 01:56 PM
03/31/07 01:56 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
I am reading 680.10 ('02 NEC) and it tells me that if the wiring is within 5 feet horizontal of the pool and it is underground the wiring methods do not include UF cable. If you are beyond 5 foot then the rules of 300.5 apply.


George Little
Re: burial depth on pool [Re: George Little] #161227
03/31/07 05:08 PM
03/31/07 05:08 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,242
Estero,Fl,usa
UF is not really recognized for any pool equipment is it? (no insulated EGC)
All the guys I know just say "no" to any wiring that is not necessary for the pool to be inside the 5' zone. The pool digger usually enforces that rule with his backhoe anyway. With the possible exception of a power cover I can't think of any other "pool" equipment that will be there besides the light.
I guess the question is whether you wire before they backfill the shell. Even if it is after, this is fresh fill, should be easy digging. On my pool I did go "after" but that was mostly to avoid stress on the plumbing that I did at the same time.


Greg Fretwell
Re: burial depth on pool [Re: gfretwell] #161238
03/31/07 07:47 PM
03/31/07 07:47 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Greg- I agree with you on the wiring in the 5 foot zone being only pool related but every once in a while I've run into a need to have wiring non pool related run in that zone due to side yard or other space limitations and I don't know what he had but if he had to run in the 5 foot zone it would have to be in conduit.


George Little
Re: burial depth on pool [Re: George Little] #161240
03/31/07 08:32 PM
03/31/07 08:32 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Greg- I just had a thought about the power for fiberoptic lighting for a pool. It is not required to be in a raceway. But it could be in the 5 foot zone and as such would have to be in conduit. It comes as hard wired and as cord and cap connected. If the latter it would have to be GFCI protected.
If it were hard wired then it could be in UF and possible not need GFCI protection I think???

Last edited by George Little; 03/31/07 08:34 PM.

George Little
Re: burial depth on pool [Re: George Little] #161262
04/01/07 02:22 AM
04/01/07 02:22 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,242
Estero,Fl,usa
How do you approve an above ground light inside the zone by code? (not "underwater")
The only time I have seen fiber illuminators they get installed outside the zone and "fibered" in. That makes everyone happy so the contractor does it that way. He gets to sell another few feet of fiber too. If you are inside that zone with a light, I am really looking for something that looks like 680.23. The same thing goes for rope light, landscape lights or anything else. That is the advantage of fiber, you can put your illuminator "out there" and still pipe in light for borders, accents, spots and anything else you would have done with rope, Malibu or whatever.
I really can't think of any pool equipment besides a light, and maybe a power cover, that needs to be in the zone.


Greg Fretwell
Re: burial depth on pool [Re: gfretwell] #161263
04/01/07 02:29 AM
04/01/07 02:29 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,242
Estero,Fl,usa
Actually not even the power cover. That electrical equipment needs to be 5' away.


Greg Fretwell
Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,156 Are you busy
185,626 Re: Forum
174,981 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.038s Queries: 16 (0.005s) Memory: 1.0278 MB (Peak: 1.2092 MB) Zlib enabled. Server Time: 2018-07-22 01:25:12 UTC