Can anyone clear this up? Section 200.6(A)states that the grounded conductor must be identified continuous. If you read further to 200.7(A)(3)states you can identify at terminations. This contradicts itself. Any help please.
200.6(A) applies to conductors #6 and smaller. 200.6(B) applies to conductors #4 and larger and 200.7(A)(3) would apply to conductors that are field marked as allowed by 200.6(B)