I'm installing a 240V 50Amp Jacuzzi at a residence. What is the minimum/maximum distances for the disconnect? Where can I find this in the NEC?

Many thanks,
Byron

Latest Labor & Material Cost Estimating Guides

Latest Labor and Material Cost Estimating Guides

#154389 07/02/05 09:50 PM
Joined: Jun 2005
Posts: 821
S
Member
Article 680.40 states: Electrical installations at spas and hot tubs shall comply with the provisions of Part I and Part IV of this article.

So, in short, the disco must be within sight and at least 5' away from the hot tubs inner wall, and not more than 10' away.

#154390 07/02/05 10:00 PM
Joined: Jul 2004
Posts: 10,043
Likes: 37
G
Member
Within sight but at least 5 feet away.

680.40 General.
Electrical installations at spas and hot tubs shall comply with the provisions of Part I and Part IV of this article.

680.12 Maintenance Disconnecting Means.
One or more means to disconnect all ungrounded conductors shall be provided for all utilization equipment other than lighting. Each means shall be accessible and within sight from its equipment.

680.22 ...
(C) Switching Devices. Switching devices shall be located at least 1.5 m (5 ft) horizontally from the inside walls of a pool unless separated from the pool by a solid fence, wall, or other permanent barrier. Alternatively, a switch that is listed as being acceptable for use within 1.5 m (5 ft) shall be permitted.