#154388 07/02/05 09:03 PM
Joined: Sep 2003
Posts: 114
B
Member
I'm installing a 240V 50Amp Jacuzzi at a residence. What is the minimum/maximum distances for the disconnect? Where can I find this in the NEC?

Many thanks,
Byron

Horizontal Ad
#154389 07/02/05 09:50 PM
Joined: Jun 2005
Posts: 821
S
Member
Article 680.40 states: Electrical installations at spas and hot tubs shall comply with the provisions of Part I and Part IV of this article.

So, in short, the disco must be within sight and at least 5' away from the hot tubs inner wall, and not more than 10' away.

#154390 07/02/05 10:00 PM
Joined: Jul 2004
Posts: 10,006
Likes: 37
G
Member
Within sight but at least 5 feet away.

680.40 General.
Electrical installations at spas and hot tubs shall comply with the provisions of Part I and Part IV of this article.

680.12 Maintenance Disconnecting Means.
One or more means to disconnect all ungrounded conductors shall be provided for all utilization equipment other than lighting. Each means shall be accessible and within sight from its equipment.

680.22 ...
(C) Switching Devices. Switching devices shall be located at least 1.5 m (5 ft) horizontally from the inside walls of a pool unless separated from the pool by a solid fence, wall, or other permanent barrier. Alternatively, a switch that is listed as being acceptable for use within 1.5 m (5 ft) shall be permitted.


Greg Fretwell
#154391 08/02/05 09:15 PM
Joined: Jan 2005
Posts: 109
L
Member
Make sure to check with your local building Dept. They change the rules some places. We get a print out from the local bld. dept. when pulling permits for spas that are a little differant than code. Rod


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Top Posters(30 Days)
Popular Topics(Views)
352,283 Are you busy
276,058 Re: Forum
255,598 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5