ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Happy Father's Day!
by Bill Addiss - 06/19/21 04:16 PM
A Risky Setup
by timmp - 06/18/21 08:08 PM
Where is Everyone?
by gfretwell - 06/18/21 11:07 AM
Conduit over Vinyl Siding
by Jim M - 06/16/21 08:30 PM
Updated Forum Software
by Admin - 06/15/21 10:23 AM
New in the Gallery:
2020 - 2021 Winter Project
2020 - 2021 Winter Project
by Bill Addiss, April 29
Garden 2021
Garden 2021
by Bill Addiss, April 26
Who's Online Now
0 members (), 6 guests, and 13 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#152046 10/30/03 01:05 PM
Joined: Oct 2000
Posts: 3,661
Likes: 1
Admin Offline OP
Administrator
Member
[Linked Image]

[Linked Image]

[Linked Image]
Quote
This is an old ground detector. The 230 volt bulbs are paired in series, 2 per phase, for used on the 480 volt system.

-Electure

#152047 10/30/03 10:06 PM
Joined: Aug 2002
Posts: 1,081
T
Member
Please explain what this is for--I don't quite follow. If a circuit came in contact with a ground, would it not trip the OCPD?

#152048 11/01/03 08:55 AM
Joined: Aug 2001
Posts: 7,520
P
Member
TG,
It would be used on an UNGROUNDED system, in this case 480V delta.

In such a system a single ground on one phase would not trip out an OCPD (but a second, simultaneous ground on another phase might).

As the first unintentional ground might otherwise go unnoticed, the ground detector is fitted to provide an indication of a ground fault.

#152049 11/01/03 05:19 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
Ungrounded-delta {or even ungrounded-wye} plant distribution has a successful history for process-interruption minimization, but if you don’t act quickly after first fault, it gets messy—potentially with two or more overcurrent devices operating simultaneously. If you want to research this further, there is a {rare} online paper about it — www.neiengineering.com/papers/paper1JN.pdf for applying such a system one has to be well aware of the first-fault limitation and the need for action when it occurs. It is very problematic if one transformer set feeds two different areas of a plant, or worse yet, two different facilities under different ownership. The tradeoffs have to be carefully understood by all when adopting this system-grounding method.

There is understandable reluctance for many utilities to provide this type of service for their customers because its limitations have to be well understood by all to be effective. It is more likely found in cases where a facility buys power from the utility at medium voltage, or “primary” service, and the plant has complete control over all distribution and loads connected to the {typically 480V or 600V ungrounded-∆} system. If the utility owns the [480-600 or up to 4160V] secondary windings—essentially the grounding “source”, then it may be a poor choice from a reliability and service-continuity standpoint. There will be regional practices and local customs, but in many cases utilities flat out refuse to serve anything except for [480Y/277V or 600Y/347V] 4-wire grounded-wye service to limit repeated ‘rat-race’ complaints and finger-pointing from their customers.

If in the case where [phase-to-neutral loads are served, like 277- or 347-volt lighting loads] the distribution system must be solidly grounded. An absolutely insane stopgap mutation in system grounding is a corner-grounded-delta arrangement, except possibly for an isolated single-transformer/single-motor configuration, for all too often that seems to cause its own set of headaches.

#152050 11/01/03 05:47 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
electure — The book page with the nippled lamps and horseshoe filaments really points out the antiquity of the system, and matches well with the apparent age of the switchboard. [Never mind the broken lamp with its handy 480V exposed-live parts.]

[Linked Image from 6l6.net]

There is a lot of this type of stuff still in service out there—however ancient, misunderstood and neglected. It’s not hard to imagine a painter tipping a ladder up to the switchboard and planting a kneecap into the broken lamp.

#152051 11/01/03 09:02 PM
Joined: Aug 2002
Posts: 1,081
T
Member
Thanks for the great explanations, gentlemen!

Quote
kneecap into the broken lamp
OUCH!!!

#152052 05/07/04 10:35 PM
Joined: Jan 2003
Posts: 18
I
Member
Us old guys worked with that fine equipment daily, we had digital wooden box meters!


Larry

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Top Posters(30 Days)
Trumpy 10
Admin 10
Popular Topics(Views)
280,435 Are you busy
213,508 Re: Forum
200,398 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5