#15091 10/13/02 07:53 PM
Joined: May 2001
Posts: 552
T
Member
sparky
I saw an ad for a backboard for meter cans to be installed on before the siding is installed.The same co.may have something for panels,but I don't remember the name.Anyone else?


Donnie
Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#15092 10/13/02 08:25 PM
Joined: Oct 2000
Posts: 4,161
Likes: 5
Member
Arlington?

[This message has been edited by Bill Addiss (edited 10-13-2002).]


Bill
#15093 10/13/02 09:21 PM
Joined: May 2001
Posts: 552
T
Member
Bill ,that sounds right. My Alzheimers was kicking in again [Linked Image]


Donnie
#15094 10/14/02 06:47 AM
Joined: Mar 2001
Posts: 2,056
R
Member
Yes, Arlington makes the meter mounting board. It's the MM series.
BTW,

They make a larger unit (MM 35?) that my local suppliers didn't carry. I would have needed to order a minimum quantity. I called Arlington and they sent me one free of charge!

#15095 11/07/02 09:32 AM
Joined: Jul 2002
Posts: 241
S
SJT Offline OP
Member
I'll have to try treated 2x4's secured to the concrete first, then the painted plywood (3/4") over that. It sounds like a real nice job.

#15096 11/07/02 01:08 PM
Joined: May 2001
Posts: 176
W
Member
If the areas you are mentioning are in a wet or damp location, and I would consider a basement in some cases to be wet and damp, then Art 384-17 (1999 Code) refers you to Art 373-2(a). That requires a 1/4" airspace between the enclosure and the wall.
Our company specs require a unistrut channels run vertical behind the panel. This allows busbar cooling by venting the air upward as in the chimney effect. It also eliminates the possibility of moisture buildup on the back side of the enclosure.

#15097 11/07/02 05:04 PM
Joined: Jul 2002
Posts: 241
S
SJT Offline OP
Member
Hello Warren,
What area is that? Sounds like a good rule.
Stay safe

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#15098 11/07/02 05:14 PM
Joined: Aug 2001
Posts: 7,520
P
Member
Most older service cutouts and meters in England are also mounted on ply, although not normally painted.

The older ones were fitted to the wall with four porcelain standoffs giving about 5/8" clearance behind.

The new outside plastic cabinets have particle board secured in the back.

#15099 11/07/02 06:36 PM
Joined: Jul 2002
Posts: 680
W
Member
I'm surprised there has not been a marketed panel 'backboard' .....


A local company is making backboards up here in Maine. Consists of plywood and 2 by 4's painted black. I forget the price and sizes?. They used to have a display in the supply house I frequent the most.

#15100 11/07/02 07:42 PM
Joined: Oct 2002
Posts: 210
S
Member
I use PT 2x4s on the flat with concrete nails and then secure the 4 x 4 sheet of 3/4" AC Ply to the 2x4s.