#14703 09/30/02 12:04 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Just to confirm my thinking, on a 208v 200a 3ph service, (providing the wire is the correct size), is good up to 200amps per phase measured with an amp clamp.
But the total would not be 600 amps, correct?


The Golden Rule - "The man with the gold makes the rule"
Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#14704 09/30/02 01:32 AM
Joined: Aug 2001
Posts: 7,520
P
Member
If you have 200A being drawn on each phase, then no, you can't really say that the total is 600A because of the 120-degree phase difference between phases. That same phase difference is the reason why if you have exactly the same current flowing on each phase then the neutral current will be zero.

#14705 09/30/02 01:52 AM
Joined: Jul 2002
Posts: 8,450
Likes: 4
Member
I would say that you are correct, it depends upon the size of your protection on the circuit and the cable size.
You would think that you could directly add the line currents together, unfortunately, this not so, [Linked Image].

#14706 09/30/02 10:07 PM
Joined: May 2002
Posts: 202
J
Member
you are correct. 200amps is what you will read on each leg but you don't add them up. It is just 200amps

#14707 10/01/02 12:31 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
If one of the legs was a 208v to grd wild or high leg, I assume it would still be the 200amp max on each leg, on a 200a service. Also correct?
Thanks for your help,


The Golden Rule - "The man with the gold makes the rule"
#14708 10/01/02 06:44 PM
Joined: Jan 2002
Posts: 324
A
Member
If your B leg is 208 to ground, you're on a delta secondary and thats actually a 240/120 delta. But youre still a 200A service. You will read 240 between phase to phase.