lighting control #143621
08/13/05 11:05 AM
08/13/05 11:05 AM
J
james S  Offline OP
Member
Joined: May 2003
Posts: 107
West England
has anyone came across flourecent lights that are dimmed down to a set level with a 24 volt dc supply?my problem is when i diconnect the dc supply from one fitting the rest of the fittings in the room go bright,which is a problem given the type of enviroment they are illuminating.my idea was to find the resistance imposed across the dc supply and replace the fitting with the same value resistor enabling me to take the fitting out of service for maintenance with the remainding fittings dimmed.
any info would be much appreciated

Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Re: lighting control #143622
08/13/05 11:58 AM
08/13/05 11:58 AM
B
britspark  Offline
Member
Joined: May 2005
Posts: 54
southampton united kingdom
James,
could you give a bit more information mate, what type of fittings, control gear manufacture etc, are the fittings all on the same dim pack ?

britspark

Re: lighting control #143623
08/15/05 07:27 AM
08/15/05 07:27 AM
P
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
Second the questions. What kind of dimmers are in use? Are they just varying the voltage or are they some kind of PWM (Pulse-Width Modulation) controller?

Re: lighting control #143624
08/15/05 11:45 PM
08/15/05 11:45 PM
A
aussie240  Offline
Member
Joined: Jul 2005
Posts: 223
Blue Mountains, NSW, Australia
If it's the electronic type of ballast with remote dimmer you're describing, the dimmer is just a typical potentiometer, so yes it could be replaced with a fixed resistor.
These ballasts rectify the incoming mains, with the resulting 340V DC fed into a high frequency (~30-100KHz) ferrite transformer via high voltage switching FET's or transistors. There's a controller IC that sets frequency and pulse width of the drive to these transistors, as well as incorporating other features like shutting down if the tube is too worn out to fire etc.
It is a more efficient way to run a fluorescent tube than an iron cored choke partly because fluoro tubes work better at hight frequencies, and also higher frequencies means less wire (ie. less voltage drop) wound on the inductive components. A further advantage is you eliminate the danger of the strobing effect near rotating machinery. The downside of these ballasts is that they're much more susceptible to damage by high voltage spikes on the mains.
The old way to dim flourescent tubes is to run them via a normal triac light dimmer and iron cored choke, but with the tube heaters permanently energised via a separate filament transformer. The range of control isn't the best...problem being that unlike an incandescent bulb, a fluoro tube needs a minimum voltage for the mercury vapour to ionise. By using the electronic ballast method you can keep the voltage high but just vary the RMS current through the tube by altering the pulse width.

[This message has been edited by aussie240 (edited 08-15-2005).]

Re: lighting control #143625
08/16/05 04:19 AM
08/16/05 04:19 AM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,236
SI,New Zealand
240,
Great comments there mate!. [Linked Image]
I agree, the older form of dimming was probably more wasteful, with respect to energy use than anything we use today.
The best thing about HF Ballasts these days is the lack of Strobo-scopic effect, as you mentioned.
Where as a few years ago, you had to have a few fittings on different phases to prevent the same thing. [Linked Image]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,156 Are you busy
185,626 Re: Forum
174,981 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.005s) Memory: 0.9693 MB (Peak: 1.1069 MB) Zlib enabled. Server Time: 2018-07-22 01:23:52 UTC