0 members (), 1,035 guests, and 11 robots.
Page 3 of 3 1 2 3
#142508 01/28/05 08:10 PM
Cool,
I'm certainly glad that that has been solved!. [Linked Image]
It's strange how a system that is installed to protect people against shock can cause a thing like this to happen.
#142509 01/29/05 05:04 PM
Indeed. Makes you wonder whether the recommended (or required-by-code) approach is always the best, doesn't it?
You would have appreciated some of the discussions I had with Bennie Palmer a couple of years ago. We exchanged a good many messages on the subject of bonding vs. isolation and grounding issues.
#142510 01/30/05 11:55 PM
Western Power came to site tonight to survey the pole,, found 18volts entering the ground around my customers house
how did they measure this`?
#142511 01/31/05 05:41 PM
Cant see this for the life of me! I would be amazed if bath water in waste could introduce earth potential, or any other potential for that matter. A 1m column of water with a high degree of disolved salts in a 15mm plastic pipe will have a resistance of circa 30,000 ohms! I can see however, that a poor neutral connection in neighbouring premises would increase potential between bonded bath and floor, which may be more representative of true earth. May be reasonable to sink spike to reduce touch voltages on pme systems where neutral problems will always exist.
regards
lyle dunn
Page 3 of 3 1 2 3
