1 members (Scott35), 542 guests, and 43 robots.
#13773 09/11/02 04:27 PM
F
Please check my math:
(22) 1500 watt metal halide light standard fixtures @208 volts, 8.2 amps each. They will be balanced on a 120/208 volt, three phase, 4 wire service.
37,523 watt load divided by 208 x 1.73=104 amps.
The load would be considered continuous thus multiply by 1.25 = 130 amps total load.
Am I correct?
Tom Offline
I dunno.
Try this, 21 fixtures installed so they balance out on all 3 phases equals 114.8 amps, add one more fixture on 2 phases brings the total to 123 amps multiply by 1.25 = 153.75 amps
you'll either need a 150 amp panel (your calculation) or a 200 amp panel (my calculation). The price difference is probably non-existant. The only cost that might matter would be the feeder size.
Frank, I did the calculation and came up with the same amperage as you did. I beleive you are correct
Each fixture - 208v x 8.2a = 1705.6 va
22 fixtures + 2 (to balance load) = 24 fixtures
1705.6 va x 24 = 40 934.4 va
40 934.4 va divide by 208 = 196.8 amps
divide by 1.73 = 113.7 amps
113.7 x 1.25 (continuous load) = 142.5 amps
Ed
Frank,
Don't forget to add (10%?) for ballasts.
F
Is that for power factor?
Tom Offline
Am I missing something? Why is everyone trying to change this calculation to volt-amps when Frank has stated that each fixture draws 8.2 amps?
Doing the Volt-Amp thing might be advantageuos if this load could be equally shared by all three phases, but since it can't, I feel the resulting answers are too low. The math is correct, so I'll assume that everyone slipped off their boots to use their toes [Linked Image] and they all did their gazintas correctly.
There will be 15 fixtures on A phase x 8.2 = 123 amps, 15 fixtures on B phase x 8.2 amps = 123 amps
C phase only has 14 fixtures x 8.2 amp=114.8 amp.
125 amps x 125% = 153.75 amps, too much for 150 amp feeder or 150 amp panel.
A 1500 watt fixture at 208 volts will draw 7.2amps continuous.Why are we talking 8.2 amps and adding 125% for a continuous load?
What am I missing?
Chris
Chris:
A 1500 watt metal halide sport light draws 8.2 amps at 208 voltsat full illumination, and 4.70 amps starting. Source of info is Lumark/Cooper Lighting.
That is a high power factor, CWA.
HotLine1
PS to Frank: Put in a 200 amp feeder and panel please!
John,
Thanks for the info.Does Lumark/Cooper have a WEB site with tech info for their products?
Chris
