0 members (), 150 guests, and 21 robots.
#137471 07/17/03 02:54 PM
Over here, ranges are exempt from RCD protection, mainly because of this Leakage current problem.
It's the same for Refrigerators,Hot Water Cylinders and Air Conditioning equipment.
With respect to ranges though, I'm not sure if it was mentioned above, but due to the heating and cooling cycles within the range body itself, during operation, there will tend to be a small, but appreciable build-up of moisture, that can slightly alter the Insulation Resistance values of the appliance, this is normal and any range that has a Minature Circuit Breaker protecting it(at the switchboard), should be fine. [Linked Image]
[This message has been edited by Trumpy (edited 07-17-2003).]
#137472 07/18/03 04:29 AM
Trumpy,
Ranges aren't specifically required to be on an RCD-protected circuit here, so long as the loop impedance and protective device(s) can meet the specified 5-second disconnect time on an earth fault.
In practice, that usually means that where the earthing system is TN-S or TN-C-S (PME, equivalent to your MEN) then an RCD is not necessary. If the TT system is employed, then the RCD becomes essential for all circuits.