Re: To: Pauluk
#132707
01/05/05 09:20 AM
|
Joined: Aug 2001
Posts: 7,520
Member
|
Yep, round my way the soil is rather sandy (well, the beach is only 200 ft. away!) so you can almost push a 4 ft. rod into the ground with your bare hands. Just don't expect a low resistance reading!
|
|
|
Re: To: Pauluk
#132708
01/05/05 06:24 PM
|
Joined: Dec 2004
Posts: 161
Member
|
D'ya think the 4 foot earth rods got anything to do with the voltage here, not having 120 Volts? Or is it just that we rely on the meaty neutral more?
|
|
|
Re: To: Pauluk
#132709
01/06/05 03:35 PM
|
Joined: Dec 2002
Posts: 1,250
Member
|
At least with RCDs you don't usually need to have 16amps or so flowing to earth/ground before something trips! ![[Linked Image]](https://www.electrical-contractor.net/ubb/smile.gif)
|
|
|
Re: To: Pauluk
#132710
01/10/05 07:16 AM
|
Joined: Aug 2001
Posts: 7,520
Member
|
D'ya think the 4 foot earth rods got anything to do with the voltage here, not having 120 Volts? I think it's probably more the case of our earthing arrangements. The only time an earth rod is required here is on a TT system, which will have an RCD, or in old installations a voltage ELCB or a current-operated ELCB of at worst about 500mA rating. In the U.S., it's normal for all services to have a ground rod installed, despite the fact that they are equivalent to what in British terms would be a PME system.
|
|
|
Re: To: Pauluk
#132711
01/10/05 08:45 PM
|
Joined: Jul 2004
Posts: 200
Member
|
In the U.S., it's normal for all services to have a ground rod installed, despite the fact that they are equivalent to what in British terms would be a PME system.
I tend to introduce rods in new works where the PME supply is o/h and there's any risk that the neutral line could be broken - ie if the supply comes on a few spans through a wood or near trees ( which around here is usual!) before grounding.
If hindsight were foresight, we'd all be millionaires!
|
|
|
Re: To: Pauluk
#132712
01/11/05 05:20 AM
|
Joined: Aug 2001
Posts: 7,520
Member
|
I think that's an excellent idea, and I've sometimes wondered why BS7671 hasn't specified earth rods on PME systems as an extra precaution.
|
|
|
Re: To: Pauluk
#132713
01/11/05 08:33 PM
|
Joined: Jul 2004
Posts: 200
Member
|
Paul, in the late eighties, a local NORWEB inspector told me I was being "over cautious and costing the customer more"...
What price a little extra safety eh?
If hindsight were foresight, we'd all be millionaires!
|
|
|
|
|