I am not familiar with these. Is it safe to assume it regulates voltage? Running through the center of the three coils is a shaft, and attached to the top of the shaft are gears which drive a chain. I am not sure what it is doing.
The nameplate on the housing reads 'Input V 240 Hz 50-60 Ph3 Output V 0-280 Amps 250 KVA 121.
Now to calculate what this thing should be fed with, I usesd the formula KVAx1000/ Voltage (240) 121x1000=121000/240=504.16
They are feeding this with a Nema5 starter using 2/0 wire. If I am calculating right, shouldnt the ampacity of the wire be based on 504?
This variable transformer than feeds an oil filled transformer with output votages as high as 36kv.
It is in a drywalled room in an office suite. According to art 450 I beleive it needs to be in a vault.
But there are 7 exceptions. I do not know the KVA of the second tranformer.
Please help!
|
|
|
|
Joined: Feb 2002
Posts: 182
Member
|
|
|
|
|
Joined: Dec 2001
Posts: 201
OP
Member
|
Thank you Bob. That was informative. I still am not sure on the feeder size. Who can tell me if I am right when using the formula? 121kva @240v is 504amps. This is currently wired with 2/0
|
|
|
|
Joined: Jul 2004
Posts: 787
Member
|
If you are single phase. --------------------------------------------------------- But since you are three phase KVA = V x A x sqr rt 3 KVA/(V x sqr rt 3) = A 121000/(240 x 1.73)= 291
|
|
|
|
Joined: Jul 2004
Posts: 101
Member
|
Yes, but if the nameplate says 250A, it is 250A. That needs to be the basis for your fusing, so the wire need only be sized for the fused circuit.
JRaef
|
|
|
|
Joined: Mar 2005
Posts: 1,213
Member
|
At the maximum voltage level of the transformer:
121kVA = 280V x 250A (3P).
To set the OCP for 291A @ 240V would allow the transformer to overload if it was adjusted to 280V. If this were a normal transformer and you could lug it to the 240V terminals, OCP can be sized for 291A, but in this case, 250A is required for safety.