#130710 10/21/06 11:57 AM
Joined: Oct 2006
Posts: 1
J
Jaz Offline OP
Junior Member
Hi all,

Can some one point me in the direction for motoer and cable amps?

I have a Q.
A 1500HP D.C. motor compound wound, reversible,
Shunt rated at 100Amps.

How do I work out total amp requirements, I believe this motor runs at 750 Volts.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#130711 10/25/06 12:54 PM
Joined: Jul 2002
Posts: 8,443
Likes: 3
Member
Exactly, what do you want to run on the end of this 1500HP motor?.
Next question would be, do you have a DC supply large enough to supply it?.


[This message has been edited by Trumpy (edited 10-25-2006).]

#130712 10/25/06 04:22 PM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
An average DC motor draws an armature current of approx 1.5A per HP at 550V.

The armature current varies inversely to the applied voltage so in your case:

1500HP * 1.5A/HP * 550V/750V = 1,650A.

#130713 10/26/06 08:30 AM
Joined: Nov 2000
Posts: 2,148
R
Member
Note that you can't use standard building wire for this application because the armature voltage is above 600 volts. I have used DLO/RHH for this application a number of times. The last 1500 hp DC motor that I worked on needed cables rated for 2156 amps (motor FLA at 1725 times 1.25 for wire size). We used the ampacity for 500 kmil derated to 344 amps because of 4 current carrying conductors in each raceway. The calculation only required 7 sets or conductors, but because of the rules in 310.4 we had to use 8 sets. We had four 4" conduits, each with four 535.3 kcmil DLO cables.
Don


Don(resqcapt19)
#130714 01/06/07 12:34 AM
Joined: Mar 2001
Posts: 345
T
Member
Out of pure idle curiosity what was a monster like that turning.
--
Tom Horne


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
#130715 01/07/07 07:18 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Tom,
The one I was working on is an extruder drive motor. That extruder is used for the final step for making ABS plastic pellets. The ABS resin and the addatives for color and other properties are fed into the extruder and and mixed and heated by the screws and forced out of the die head in about 130 3/16" strands that are then cooled in a water bath and sent to a pelletizer to cut them in to pellets about 3/16" long and then bagged, boxed or bulk shipped to the customer who will mold the plastic into a final product.
By the way those 8 535.3 kcmil DLOs were connected to 4 4/0s in the motor junction box. We had to add a box extension and a bus detail to make the transition from the size of wire required by the code to the internal motor armature leads.
Don


Don(resqcapt19)