ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Photo of the Week:

Old Fused Panel
 Old Fused Panel

Advertisement:-Left
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 27 guests, and 35 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Jun 2004
Posts: 7
L
Junior Member
Three generators (1000KVA,800Kw,415V)are running in parallel almost on 500Kw each,but generator A is variating form 50 to 1500Kw when it runn on 400Kw (this was measured on recorder,it measures the both min & max vales) while the actuator voltages are constatnt.Please tell me the cause of load hunting.

Horizontal Ad
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
When 'A' is hunting, are the other two gens compensating by picking up excess load?
How are you accounting for load sharing among the three gens?


Ron
Joined: Jun 2004
Posts: 7
L
Junior Member
No,two other generator pick up load only when speed drops of any one,there is no variation in speed,i already told that actuator voltage of A are constant.load sharing is controlled by 2301A woodward speed sharing and load control unit.

[This message has been edited by luckyali (edited 07-08-2004).]

Joined: Apr 2002
Posts: 2,527
B
Moderator
If you have studied the Woodward instruction book and not resolved the problem, you might contact their technical-support group. From a distance, it is hard to tell whether it is a configuration problem or one internal to the Woodward components.

Joined: Jul 2004
Posts: 200
U
Member
Sounds to me like a synchronising issue - definitely a sharing/control matter. Speed variation in gennys? Hmm. If a diesel set hunts its generally an injection pump governor problem, or the same for petrol but on the carb. However, this would result in cyclic problems and a host of other evils - and dropping like flies of breakers.

Several years ago I got up one morning to find the lights fluctuating from about 50% to full on roughly 2.5cps. The tv didn't like it at all!! [Linked Image] This lasted about ten minutes before we had a 30 second outage then back to normal. A few days later I saw our chief utility troubleshooter in the village and asked him what it was about. His reply was that it was something that theoretically couldn't happen; the ( at that time ) two alternators supplying our region ( we were disconned from the national grid for repairs over the weekend ) had got out of sync with each other; the control system had crashed. I never stopped to work it out, but I guess it is theoretically possible, especially if balancing/motive force is not up to scratch.

Call up the load-box suppliers [Linked Image]


If hindsight were foresight, we'd all be millionaires!

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Top Posters(30 Days)
BigB 4
Popular Topics(Views)
327,804 Are you busy
252,662 Re: Forum
235,293 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5