#127812 01/08/02 07:08 PM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
I'm doing a job at a auto repair garage that has a 400 amp 3ph panel. Reading the voltages I got 120v to ground on all 3 phases and between phase A & B it read 215v, B & C was 215v, but A & C was 0 volts. I have never come across this before. Also not sure why I got 215v between phases instead of 208v or 230v. Transformer problems? Any ideas? Thanks..
Al D


The Golden Rule - "The man with the gold makes the rule"
Joined: Oct 2000
Posts: 5,392
S
Member
Al,
drop a phase? x-former crapped out? check the draw on yer motors....single phasing should pop a few OL's ??

Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
I found the problem last week on the wrong 3ph voltage readings. The customer had some so-called electricians out to do some work previously and they shorted something and blew one of the 3 legs (Phase A) at the meter where the panel was fed from, and they could'nt figure it out so they tied the circuits that were off to breakers on the other working phases just to get it working.
The reason I was getting reading on all 3 phases is it was being backfed through some load. Hard to believe someone could do this and then cover it up and leave it because they couldn't figure it out. It was a new Meineke Muffler business and wasn't open yet so the customer would'nt have noticed more problems until later.


The Golden Rule - "The man with the gold makes the rule"

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles
Posts: 349
Joined: April 2004
Top Posters(30 Days)
BigB 4
triple 3
Popular Topics(Views)
303,012 Are you busy
232,123 Re: Forum
216,775 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5