You said the main blew. I think we are to assume that it was a non-GFI circuit breaker that opened with no damage.
Did both have the same interruptor rating?
If the load through the main was already running 200 A before the fault occurred, it is imaginable. The 20 A CB was cold and the 200 A CB was already warmed up.
Dspark, Bill, It happened when the 20A was turned on, the panel is new, not loaded up as yet, did not amp it out but should be about 40A usage give or take.
The interupter rating should be more for the main, however, as you pointed out, there was a hand holding the 20A !
I had an apprentice miswire a switched leg... wired it like a switch loop... dead short. I should have been watching him closer...
New House, very little load on the main. The SQ D 100A main tripped before the 15A lighting CB. I replaced the SQ D 15A breaker while the appy rewired the switch (correctly this time).
I never had a good explanation either, but I didn't take any chances... Breakers can be bad out of the box... Even SQ D
-Virgil Residential/Commercial Inspector 5 Star Inspections Member IAEI
It is my understanding that the short circuit trip curves for most breakers 200 amps and less are almost identical and with the normal manufacturing tolerances it is not unusual for a main to trip out before a smaller branch breaker on a short circuit. Holding the handle of a breaker has nothing to do with its trip time. The breaker will open in the same time even if the exterior handle does not move. Don(resqcapt19)