Dead Shorts #127093
04/26/01 08:55 PM
04/26/01 08:55 PM
S
sparky  Offline OP
Member
Joined: Oct 2000
Posts: 5,371
Had a 200A 3 ph 208Y120V main blow today due to a dead short in a 20A circuit.

The spike must have had sufficent duration to do this

But the 20A breaker never tripped, and i am at a loss as to explain this
[Linked Image]

any input apprectiated

Tools for Electricians:
Re: Dead Shorts #127094
04/26/01 11:02 PM
04/26/01 11:02 PM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,903
NY, USA
Sparky,

I've seen the same thing happen. I always thought that maybe the main was more sensitive somehow to the characteristics of a dead short.

Bill

Re: Dead Shorts #127095
04/27/01 12:44 AM
04/27/01 12:44 AM
A
Anonymous
Unregistered

You said the main blew. I think we are to assume that it was a non-GFI circuit breaker that opened with no damage.

Did both have the same interruptor rating?

If the load through the main was already running 200 A before the fault occurred, it is imaginable. The 20 A CB was cold and the 200 A CB was already warmed up.

Re: Dead Shorts #127096
04/27/01 01:56 AM
04/27/01 01:56 AM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,903
NY, USA
Sparky,

Did it happen when you/someone turned on the 20A breaker?

Re: Dead Shorts #127097
04/27/01 05:03 AM
04/27/01 05:03 AM
S
sparky  Offline OP
Member
Joined: Oct 2000
Posts: 5,371
Dspark, Bill,
It happened when the 20A was turned on, the panel is new, not loaded up as yet, did not amp it out but should be about 40A usage give or take.

The interupter rating should be more for the main, however, as you pointed out, there was a hand holding the 20A !

So, somehow the main saw enough AIC ?

Does this make sense?

[Linked Image]

Re: Dead Shorts #127098
04/27/01 09:32 AM
04/27/01 09:32 AM
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
I had an apprentice miswire a switched leg... wired it like a switch loop... dead short. I should have been watching him closer...

New House, very little load on the main.
The SQ D 100A main tripped before the 15A lighting CB. I replaced the SQ D 15A breaker while the appy rewired the switch (correctly this time).

I never had a good explanation either, but I didn't take any chances... Breakers can be bad out of the box... Even SQ D


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: Dead Shorts #127099
04/27/01 05:42 PM
04/27/01 05:42 PM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,903
NY, USA
Sparky,

That's what I was wondering about. Maybe the hand holding it had something to do with the Main going before the 20A.
Just fishin'

[Linked Image]
Bill

Re: Dead Shorts #127100
04/27/01 08:17 PM
04/27/01 08:17 PM
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
I see what Bill's getting at... in fact, yes, being a dead short, my hand was forcing the CB closed at the time...


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: Dead Shorts #127101
04/27/01 10:02 PM
04/27/01 10:02 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
It is my understanding that the short circuit trip curves for most breakers 200 amps and less are almost identical and with the normal manufacturing tolerances it is not unusual for a main to trip out before a smaller branch breaker on a short circuit. Holding the handle of a breaker has nothing to do with its trip time. The breaker will open in the same time even if the exterior handle does not move.
Don(resqcapt19)


Don(resqcapt19)
Re: Dead Shorts #127102
04/28/01 08:25 PM
04/28/01 08:25 PM
S
sparky  Offline OP
Member
Joined: Oct 2000
Posts: 5,371
Don,
thanks, i was wondering about those breaker locks on the fire breakers....

this has me wondering about series fault..

[Linked Image]

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Admin
Admin
NY, USA
Posts: 3,524
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
Popular Topics(Views)
251,615 Are you busy
188,750 Re: Forum
178,460 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.035s Queries: 15 (0.008s) Memory: 1.0228 MB (Peak: 1.2011 MB) Zlib enabled. Server Time: 2018-11-19 21:57:14 UTC