Mission impossible ?! #12601
08/12/02 09:44 PM
08/12/02 09:44 PM
M
makyts  Offline OP
Junior Member
Joined: Aug 2002
Posts: 2
chicago,il,USA
In existing multifamily dwelling (the action is taking place in Chicago) the part of service entrance conduit (circle area on the pictures bellow) has been eaten by rust. The building is ( and has to be ) occupied and has to survive 6 months without replacing that service conduit. Service is life front, building is 80 years old, so replacing conduit means :
1)replacing both service conduits, replacing the old service, and old feeders
2)new service conduits, new service, and new feeders size has to be according to new standards NEC2002 AND CEC2002
so this is classic “chain reactions” or (...)
Wires are also very old (around 80 years !? ) and covered with asphalt type insulation
So far nothing has happened ( no major fireworks ) but I think the clock is ticking…

Any ideas how to temporary protect ( against : rain, snow , and unforeseen events) that rusted area ?


Regards

makyts

[Linked Image]
[Linked Image]
[Linked Image]

Work Gear for Electricians and the Trades
Re: Mission impossible ?! #12602
08/12/02 10:47 PM
08/12/02 10:47 PM
E
electric-ed  Offline
Member
Joined: Jul 2002
Posts: 175
Canada
On a day when the area is thoroughly dry, blow out the dirt and debris with air, carefully fill the rusted out cavity with silicone caulk.
Then build a form and pour a concrete "block" over the area for physical protection.

Ed

Re: Mission impossible ?! #12603
08/15/02 06:06 PM
08/15/02 06:06 PM
T
The Watt Doctor  Offline
Member
Joined: Dec 2001
Posts: 435
Mont Belvieu, TX
Ed has a good idea. Let me throw another one your way. I would build a box or chase around the conduits, and attach it to the wall. IMHO if those conductors are going to "blow up" in the next 6 months, they are going to do it no matter what you do to try to prevent it. I wouldn't be as concerned about a phase to phase fault as I would a phase to ground fault that energizes one of the service entrance conduits.
I think I would call the City of Chicago electrical inspections department, and have an inspector come out to have a look at it with you. Tell him your situation, and I'm sure that y'all can come up with a solution.

This message will self destruct in 5 seconds,
Doc


The Watt Doctor
Altura Cogen
Channelview, TX
Re: Mission impossible ?! #12604
08/15/02 06:49 PM
08/15/02 06:49 PM
S
smokey  Offline
Member
Joined: Apr 2001
Posts: 41
cctxusa
if i was u i would not touch anything i would not want to be held liable if some fireworks do start and cause a fire sometimes it is better to just walk away if they do not allow u to fix it the wright way dont do anything at all


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
richard
richard
L.I. New York
Posts: 98
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
djk 2
Popular Topics(Views)
251,553 Are you busy
188,713 Re: Forum
178,422 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.9606 MB (Peak: 1.0906 MB) Zlib enabled. Server Time: 2018-11-18 02:35:50 UTC