2 Inch PVC Riser thru Soffit #123310 03/15/06 06:35 PM
Joined: Oct 2000
Posts: 3,647
Admin Offline OP
Administrator
Member
Quote
In our area, the POCO requires 2.5 inch gal conduit on these two service riser's

- richard
[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]

Tools for Electricians:
Re: 2 Inch PVC Riser thru Soffit #123311 03/15/06 07:31 PM
Joined: Jan 2006
Posts: 558
R
Rewired Offline
Member
2 1/2" Galvo!
Really? What I see there is the norm around here, not sure i like how close the weatherhead and connections are to that downspout in the one picture though..

A.D

Re: 2 Inch PVC Riser thru Soffit #123312 03/15/06 08:47 PM
Joined: Feb 2006
Posts: 9
T
TNTELECTRIC Offline
Junior Member
that would never get passed around here. Were is this located? Here the only place you can use pvc is on a pole.

tom

Re: 2 Inch PVC Riser thru Soffit #123313 03/15/06 08:56 PM
Joined: Nov 2001
Posts: 42
A
alan bergold Offline
Member
this is most definetly long island area nassau/suffolk this is fine practice and is commomly used as a service means in this area . that is a lever bypass meter pan ,and is the only one acceptable under lipa jurisdiction


JBIELECTRIC EAST MEADOW NY
Re: 2 Inch PVC Riser thru Soffit #123314 03/16/06 03:29 AM
Joined: Oct 2005
Posts: 29
N
Navyguy Offline
Member
I certainly don't think it would get passed around here either...

Service Entrance too close to front window, and downspout, Meterbase not 1 meter from the corner.

It seems to be all the way down the block however. I think I would have went underground.

By the way, is not that bay window in the second pic upside down...

Re: 2 Inch PVC Riser thru Soffit #123315 03/16/06 07:23 AM
Joined: Aug 2001
Posts: 329
S
Steve Miller Offline
Member
I did one last year that had 3 350s (CU)and we used 3" or 3 1/2" (being old I have no memory) PVC. POCO had no prob with it as long as it had enough straps and did not project above the roof (no PVC masts).

[This message has been edited by Steve Miller (edited 03-16-2006).]

Re: 2 Inch PVC Riser thru Soffit #123316 03/16/06 10:57 AM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Another great reminder to have a copy of the local PoCo rules! While here it wouldn't be allowed, I must say it looks a lot better than the pics we've seen of SE tacked to the walls!

Oh, BTW....they did a great job of getting vinyl siding to match the pipe:-)

Re: 2 Inch PVC Riser thru Soffit #123317 03/16/06 01:10 PM
Joined: Mar 2005
Posts: 1,803
Alan Belson Offline
Member
From this side of the 'pond' it looks horrible, and quite defaces an otherwise fine house. Or houses actually, as the close-ups are a mix of shots of the neighboring house [?] as well, [ the eaves terminations are different in the close-ups, one has a hip termination, the other a barge-board* end ]. Why could it not have been run parallel to the downspout on the hipped version, or down the corner on the other, till it penetrated the eave, then run under the soffit to a 90 bend then down to the meter? Or is that not allowed by Code?
I take it the extraneous cables draped round the meter box are temporary.

I like the bay window arrangement BTW, it has a nice symmetry with the portico.

Is the manly young fellow waving a set of giant pie-cutters for any particular reason? I know American Portion Size is out of control, but that is ridiculous! [Linked Image]

Alan

ps. Pardon if my terminology for roof styles does not translate.


Wood work but can't!
Re: 2 Inch PVC Riser thru Soffit #123318 03/16/06 01:53 PM
Joined: Dec 2004
Posts: 1,064
D
Dnkldorf Offline
Member
Just gotta ask, why didn't the riser go straight up, and the triplex get mounted in a higher position? What was the need for the 90's?


Dnk...

Re: 2 Inch PVC Riser thru Soffit #123319 03/16/06 06:20 PM
Joined: Aug 2003
Posts: 99
richard Offline
Member
those cookie cutters are ducting for a/c units, and the reason you have to use gal pipe is some people had used the soffit area to go into a splice box and steal power from the poco. The two house's were next to a house our company were working on, more pics to follow.

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sbi
sbi
indiana
Posts: 47
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 18
Admin 10
Popular Topics(Views)
279,049 Are you busy
212,153 Re: Forum
199,180 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3