#121320 07/05/05 12:45 AM
Joined: Jul 2002
Posts: 8,407
Likes: 2
Trumpy Offline OP
Member
Submitted by renosteinke:

Quote
For some reason, the PoCo ran two sets of wires- a set of 2/0 and a set of #2 for one service. You can see how the wires are spliced.
Ordinarily, there would be two insulated wires for their 120/240 service, as well as the bare ACSR neutral.

[Linked Image]
Close Up

Joined: Jul 2002
Posts: 8,407
Likes: 2
Trumpy Offline OP
Member
Hmm,
I always thought that PoCo's were all for saving every cent possible?.
{I know the one I work for does!!} [Linked Image]
The extra wires wouldn't by any chance be for future expansion would it?.
Is this a Residential or Commercial installation?.

{Message edited to add some missing letters} [Linked Image]

[This message has been edited by Trumpy (edited 07-05-2005).]

Joined: Jan 2005
Posts: 5,316
Cat Servant
Member
The location is commercial, with separate meters for two stores. Below the mast is a gutter, with taps to four meters (each business has separate meters for the hot water), so this service has been there a while.

Despite there actually being two services, the practice here is to use a gutter to tap off of one set of wires. That is what was done here.

Future expansion? The PoCo would upsize the transformer, and run larger wires.
Parallel feed? The PoCo would run wires of the same size. Different sizes run in parallel are, well, a really stupid thing to do. (If someone out there doesn't understand 'why," speak up and we'll explain it!)
The method of connection is concealed by the tape over the splices. The usual connector here is a "parallel groove" type, with grooves for two wires, not three. PoCo rules do not allow the use of split bolts.

The PoCo itself is a little confused as to how this happened. When they fix it, I'll have a Sunday service change to do.

Joined: Oct 2004
Posts: 265
D
Member
Its easy to figure out, the PoCo is stealing electricity from itself!!! [Linked Image]

Joined: Jun 2005
Posts: 821
S
Member
(If someone out there doesn't understand 'why," speak up and we'll explain it!)

Ok, I'll bite because I don't know everything.

I understand that it's wrong, but why?

Btw, what does POCO stand for?

[This message has been edited by ShockMe77 (edited 07-22-2005).]

Joined: Jul 2004
Posts: 145
C
Member
PoCo = Power Company

Got me for a few weeks when I first joined the forum too [Linked Image]

Joined: Mar 2005
Posts: 1,803
Member
Did'nt 'sparky 66' coin the word POCO?


Wood work but can't!
Joined: Jan 2005
Posts: 5,316
Cat Servant
Member
The reason this is wrong is because of voltage drop.
Ohm's law tells us that voltage equals the current times the resistance.

Let us assume, for the sake of this discussion, 200 amps flowing, at 120 volts (to ground) over 100 feet.
For #2 wire, table 8 in the NEC give a value of 0.0194 ohms resistance for this length. 200 amps x .0194 = 3.88 volts "dropped". Of the 120 volts that leaves the pole, only 116.12 makes it to the meter.

For 2/0, the value given is 0.00967. 200 x .00967 = 1.934. So, at the meter, 118.066 volts are received.

Wait- one wire is delivering 116 volts, and the other is delivering 118? Right- there's a 2 volt difference.
And, since voltage flows from higher to lower, two volts (400 watts) will flow into the smaller wire.

400 watta is a significant amount of heat generated where these wires meet.

That is why we use identical size- both in diameter and length- for parallel feeds. We eant to avoid setting up this type of situation.

Joined: May 2005
Posts: 177
J
Member
Reno, I don't understand your explanation.

You've described 200 A flowing in each wire, but in fact, the 200 A would be divided between the two according to the ratio of their impedances.

Given your example, that ratio is (.0194 / .00967) = 2:1, so 133 A of that 200 A would flow in the 2/0, and 67 A in the #2. The voltage drops therefore are equal, and there's no power "flowing" from one wire to the other.

Argument #2: A 2/0 wire is made up of 19 strands. Isn't that the same as an 18-strand wire in parallel with a 1-strand wire?

Joined: May 2005
Posts: 16
S
Member
That's the way the PoCo used to do years ago when they were doing away with residential 3 phase around here and we were replacing the old 3 pase A/C's with new single phase units.
They would parallel the two old service drops into one single phase drop.



[This message has been edited by SparksNmore (edited 07-24-2005).]

Page 1 of 2 1 2

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Top Posters(30 Days)
dsk 7
Popular Topics(Views)
284,761 Are you busy
217,372 Re: Forum
203,712 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5